Any links by chance? Sounds interesting
ISBN 0 9538972-1-4
Any links by chance? Sounds interesting
One of our regular service accounts has some branch circuit hots and neutrals scrambled between conduits. No smoke, no fire, no shocks. Sure it needs to taken care of, but it has been that way longer than I have been alive.Inductive heating, power quality, voltage gradients, EMF, shock hazards...
Anyone with real world experience will tell you conduit heats up when the net current isnt zero.
Anyone with real world experience will tell you conduit heats up when the net current isnt zero.
You continue the claim all my facts are opinions. I have proof the back them up, but you refuse to accept it.
When Tony brought up RCDs you fled because you knew he would discredit your statement regarding nuisance tripping.
Ditto when I posted docs to back up my statement magnetic trip provides arc fault protection from an NRTL standpoint.
I do see a lot of ego driven behavior on your part, however assuming so on my part is a mistake as that is not my intent. I am not driven by ego,
Do I need to go back and quote how many times someone has said X will never work only to then post documentation proving it does?
As I said, the statistics of tripping GFP and open EGC are out there.
For example, main RCDs you will tell me that the fact they use them in Europe is all the proof we need to justify main or sub main GFP here. That's your proof, that and your personal feelings.
When people point out that sub main GFP at the trip levels you advocate would cost the consumers more you simply ignore that or try to say troubleshooting won't be needed]
I refuse to believe the fact an item or test procedure exists is a reason to mandate into code
Of course. Our system was not so broken as to require AFCI's in the first place.
Nor do we need:
-Insulation testing
-Ground loop impedance testing
-Whole house GFP
-Gimmicky devices that detect heating at splices and wiring devices
We have a good, safe and reliable system that has worked for a long time now. The trouble starts when people invent and legislate products that are a solution to a problem that doesn't exist.
Tony asked me the exact same question not more than a couple of weeks ago, he asked I answered and then he asked again in this thread. I am not going to keep answering the same question.
The problem does exists plenty as stated by professional who have replied to this post.
Where's the proof that the current system is safe and reliable ???
A fire developed in a panel just last week in my neighboor. The cause determined was loose breaker jaws.
Anyone who has worked in the trade a long time has seen this problem happen countless times. ELit testing would pick out this problem before it occurs.
My ears are ringing!!! The problem does exists plenty as stated by professional who have replied to this post. Where's the proof that the current system is safe and reliable ???A fire developed in a panel just last week in my neighboor. The cause determined was loose breaker jaws. Anyone who has worked in the trade a long time has seen this problem happen countless times. ELit testing would pick out this problem before it occurs.
I have to guarantee:
The volt drop due to impedance won’t affect the operation of the circuit protection
The circuit protection is capable of performing its function
The protection will operate within specified times
The volt drop due to impedance won’t affect the operation of the circuit protection
The circuit protection is capable of performing its function
The protection will operate within specified times
For the simple reason you can’t answer the question.
During my years of study, if I couldn’t answer a theoretical question I’d do some research and find an answer.
Design work isn’t a matter of joining the dots with wire of a certain size.
I have to guarantee:
The volt drop due to impedance won’t affect the operation of the circuit protection
The circuit protection is capable of performing its function
The protection will operate within specified times
There's is no way that you can guarantee or even confirm that the circuit protection device even functions to trip. Since there is no ELit test
performed after the device has been installed to see if it's operating within manufacture specified time limits
A fire developed in a panel just last week in my neighboor. The cause determined was loose breaker jaws. Anyone who has worked in the trade a long time has seen this problem happen countless times.
Is the sky really falling or is this just a bird taking a dump...........
Hmm, but if I recall correctly the CEC does not worry about net current until the circuits are over 200 amps.
Does that mean they do not have any real world experience or does that mean it's not that big of a deal?
Design work isn’t a matter of joining the dots with wire of a certain size.
I have to guarantee:
The volt drop due to impedance won’t affect the operation of the circuit protection
The circuit protection is capable of performing its function
The protection will operate within specified times
Can you post what section you are referring to?