Low and high voltage in the same conduit
Yeah, I know and we've talked about "rolling your own" before. But the more I think about it I can't see why it wouldn't be. The LV is separated from the line voltage conductors in it's own listed 600V cable assembly.
I might be missing something but I'm not seeing anything that would prohibit it.
-Hal
Because the rule only permits that were the either the power or low voltage conductors are in a non-metallic sheathed cable. The only cable type that you can buy that is listed as having a non-metallic sheath is NM. The language in 725.136 needs to be changed as the jacket on tray cable provides at least as much protection as the jacket on NM.
Code section please.
-Hal
I cited the section in my comment.
725.136(I)
(1) Either (a) all of the electric light, power, Class 1, non–power-limited fire alarm and medium-power networkpowered
broadband communications circuit conductors or (b) all of the Class 2 and Class 3 circuit conductors are in a raceway or in metal-sheathed, metal-clad, non–metallic-sheathed, or Type UF cables