kbardonski
New member
I cant seem to find the actual code articles that say how far overhead stapling/strapping of low voltage cables (tv, phone, fire alarm). what is/are the code article(s) and what is the distance?
Do you have a code section to support your statement?4 1/2 feet. End of story. But you can get away with murder if it is not new construction.
The NEC is concerned with safety and the protection of life and property. Low voltage wiring, except as noted in Art 725 is inherently safe. How such wiring is supported is not a safety issue so it is not something you will see addressed by the NEC. Rather it is a design issue that you will have to look to the cable manufacturers for, or as has been stated the EIA/TIA or BICSI for guidance.
-Hal
It depends on the type of low volt cable you are installing. Check the manufacturers information listing.
It is a code issue, not just a mfr install spec.
Run your cable ontop of the tiles, and watch the inspector tell you it has to be supported every 54" independently of the grid support wires. Now whether you choose to run within six inches of magnetic ballasts, now thats up to you.
But the NEC does prohibit us from laying them on the grid of a dropped ceiling.
That section does leave a loop hole. It is closed in some of the other Chapter 7 articles where they reference 300.11, but is not closed in Article 725.725.21 says "Access to electrical equipment shall not be denied by an accumulation of wires and cables that prevent removal of panels, including suspended ceiling panels."
This does not seem to restrict a few cables laying on a drop tile ceiling as long as you could remove the tile.
I am not saying I would do this but it does seem to leave a loop hole in the code.:roll:
Or am I completely wrong here?