I need to ground multiple transformers to earth. Each unit requires a #2. How do I calculate the wire size needed to ground (4) of these units together?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The GEC would only need to be sized for one transformer (the largest), it wouldn't matter how many you are tieing to the GES.

Roger
 

raider1

Senior Member
Staff member
Location
Logan, Utah
The GEC would only need to be sized for one transformer (the largest), it wouldn't matter how many you are tieing to the GES.

Roger

Actually if you are connecting multiple separately derived systems to a single grounding electrode conductor the common grounding electrode must be a 3/0 and the taps to each transformer can be sized for each transformer.

Check out 250.30(A)(4) (2008 NEC)

Chris
 

pete m.

Senior Member
Location
Ohio
It appears you are asking about sizing the GEC for multiple SDS's. If this is the case 250.30(A)(4) would be a good place to start. In this section it is permissible to use taps (sized based on the derived phase conductor) to a common GEC. The common GEC is required to be minimum 3/0 coper or 250kcmil AL.

Pete
 

pete m.

Senior Member
Location
Ohio
Actually if you are connecting multiple separately derived systems to a single grounding electrode conductor the common grounding electrode must be a 3/0 and the taps to each transformer can be sized for each transformer.

Check out 250.30(A)(4) (2008 NEC)

Chris

Always typing too slow... :)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Actually if you are connecting multiple separately derived systems to a single grounding electrode conductor the common grounding electrode must be a 3/0 and the taps to each transformer can be sized for each transformer.

Check out 250.30(A)(4) (2008 NEC)

Chris

You are correct Chris, I was posting before coffee. :mad:

Roger
 