shadyone72

New member
I need to ground multiple transformers to earth. Each unit requires a #2. How do I calculate the wire size needed to ground (4) of these units together?
 
The GEC would only need to be sized for one transformer (the largest), it wouldn't matter how many you are tieing to the GES.

Roger
 
The GEC would only need to be sized for one transformer (the largest), it wouldn't matter how many you are tieing to the GES.

Roger

Actually if you are connecting multiple separately derived systems to a single grounding electrode conductor the common grounding electrode must be a 3/0 and the taps to each transformer can be sized for each transformer.

Check out 250.30(A)(4) (2008 NEC)

Chris
 
It appears you are asking about sizing the GEC for multiple SDS's. If this is the case 250.30(A)(4) would be a good place to start. In this section it is permissible to use taps (sized based on the derived phase conductor) to a common GEC. The common GEC is required to be minimum 3/0 coper or 250kcmil AL.

Pete
 
Actually if you are connecting multiple separately derived systems to a single grounding electrode conductor the common grounding electrode must be a 3/0 and the taps to each transformer can be sized for each transformer.

Check out 250.30(A)(4) (2008 NEC)

Chris

Always typing too slow... :)
 
Actually if you are connecting multiple separately derived systems to a single grounding electrode conductor the common grounding electrode must be a 3/0 and the taps to each transformer can be sized for each transformer.

Check out 250.30(A)(4) (2008 NEC)

Chris

You are correct Chris, I was posting before coffee. :mad:

Roger
 