Well, let's work it through.
-Section 250.24(B) has us using the MBJ to connect the EGCs and enclosure to the grounded conductor.
-250.24(C) has us using the MBJ to connect the enclosure to the grounded conductor.
-Art 100 definition has us using the MBJ to connect the EGC to the grounded conductor.
All three similar descriptions have us connecting the grounded conductor to some combination of the enclosure and/or the EGCs with the MBJ. If the terminal strip for the grounded conductor can be considered similar to a "bus" per 250.28(A) the common method would be compliant. I think that it is, and that may be our best way out.
If not though, and one uses a factory supplied screw or offset bar to bond the grounded terminal bar to the enclosure, and installs a separate EGC bar, we have two options.
1. Install the correct size wire, bus, or screw between the grounded conductor directly (with a split bolt or similar) and the EGC bar, or
2. Accept that the enclosure material is the second "suitable conductor" between the grounded and grounding conductor(s).
In either case, the grounded conductor is often connected to a terminal bar. If you accept the factory supplied MBJ (screw or bar), then for some short distance, you are accepting that the strip with lug qualifies as a MBJ bus, at least from the source terminal to the bonding connection. If that is so, the the EGCs are in fact connected to the MBJ bus.
-Section 250.24(B) has us using the MBJ to connect the EGCs and enclosure to the grounded conductor.
-250.24(C) has us using the MBJ to connect the enclosure to the grounded conductor.
-Art 100 definition has us using the MBJ to connect the EGC to the grounded conductor.
All three similar descriptions have us connecting the grounded conductor to some combination of the enclosure and/or the EGCs with the MBJ. If the terminal strip for the grounded conductor can be considered similar to a "bus" per 250.28(A) the common method would be compliant. I think that it is, and that may be our best way out.
If not though, and one uses a factory supplied screw or offset bar to bond the grounded terminal bar to the enclosure, and installs a separate EGC bar, we have two options.
1. Install the correct size wire, bus, or screw between the grounded conductor directly (with a split bolt or similar) and the EGC bar, or
2. Accept that the enclosure material is the second "suitable conductor" between the grounded and grounding conductor(s).
In either case, the grounded conductor is often connected to a terminal bar. If you accept the factory supplied MBJ (screw or bar), then for some short distance, you are accepting that the strip with lug qualifies as a MBJ bus, at least from the source terminal to the bonding connection. If that is so, the the EGCs are in fact connected to the MBJ bus.