Could someone please tell me what article and section allows neutrals and grounds of branch circuits being installed together in main panel, and seperated in sub-panels?
Hmmm... I believe you have that backwards....we derive the grounding from the grounded. ...
It is not so much that the grounded (usually a neutral) and the grounding conductors are allowed together in a main panel, as that is the point that we derive the grounding from the grounded.
Hmmm... I believe you have that backwards.
Hmmm... I believe you have that backwards.
I don't think so. Am I missing something?
Rob, Smart is correct, the grounded conductor doesn't exist until the system grounding (earthing) is done, so "grounded" is derived from "grounding".
However, I think the topic is "bonding"
Roger
Actually the grounded conductor is brought to the service disconnecting means from the utility. It is already grounded/earthed at the source (unless the copper was stolen for scrap :grin.
The premises system grounding conductors are bonded to the grounded. So we don't have to say derived, but grounded comes first.
No, we may not even be talking about a POCO service, (even though the term Main Panel is used) we could be talking about an SDS or a corner grounded Delta. The grounded conductor doesn't exist to us until we as the installers earth it, what is upstream of the service point is unknown to us.
Roger
It doesn't have a grounded conductor until we earth it.You even proposed the possibility of a "corner grounded Delta". Still has a conductor grounded at the source.
No, we attach to the sources center tap, and even though we know that it is the grounded conductor from the POCO, our side (the NEC side) is where we have to look and establish it for our purposes.We won't attach the three phase legs blindly at the service point, but rather the building "white" will be connected to the source's grounded phase leg,
Which can only happen after we have earthed a conductor to establish it as a grounded conductror.of which for a grounded service, must be brought to the service disconnect. 250.24(C).
On occasion, I suppose, but usually the secondary is earthed at the pole (for O/H distribution).It doesn't have a grounded conductor until we earth it.
Not the center tap for a corner ground, but a phase leg.No, we attach to the sources center tap, and even though we know that it is the grounded conductor from the POCO, our side (the NEC side) is where we have to look and establish it for our purposes.
Which can only happen after we have earthed a conductor to establish it as a grounded conductror.
Roger
We better pick the right one .
I am not aware of any multi grounded deltas supplied by any POCO, do you know of any?
Roger
While that may be true, if we are going to include the utility service, then we must also include how it affects the issue... we can't just say one of the conductors is grounded and therefore it came first... because it didn't in reality; it is grounded as a result of of earth grounding at the source end. The grounded conductor can be first only if we choose to blind ourselves to the reality.I'd tend to side with Volta, that the utility service includes a grounded conductor, rather than the idea that the utility service comes with a bunch of conductors, and that none of them are grounded until we make the bond.
...
Could someone please tell me what article and section allows neutrals and grounds of branch circuits being installed together in main panel, and seperated in sub-panels?
How about we start with 250.24(A)(5) and 250.30(A).
Agreed. By calling the grounded conductor first, I am solely speaking of the premises system. When the OP wrote "neutrals" and "grounds", I assumed, safely I think, that Grounded and Equipment Grounding Conductors were the subjects of discussion.While that may be true, if we are going to include the utility service, then we must also include how it affects the issue... we can't just say one of the conductors is grounded and therefore it came first... because it didn't in reality; it is grounded as a result of of earth grounding at the source end. The grounded conductor can be first only if we choose to blind ourselves to the reality.
Maybe, but not neccessarily so with distribution.AFAIK, transmission lines have no grounded conductor.
Either side, of course.So any grounded conductor on the customer side of transmission lines is a result of earth grounding.
Hmmm. In 250.28(A), can the grounded conductor terminal strip be considered "similar suitable conductor" to a bus? I that think between Art. 100 definition of MBJ (for the EGCs) and the installation direction of 250.24(C) (for the disconnect enclosure) some rewording is due. I'll have to think about that one. If you are right, we need a lot more EGC bars in this world!Getting back to the original discussion, it is technically a violation (IMO :roll to land EGC's on the Neutral bars of the main panel. However, you will not find this violation explicitly written in the Code. It is only through deductive reasoning I can surmise it to be a violation. In contemplating my assertion, consider this: As a result of the requirements for an MBJ/SBJ, all ground fault currents must pass through the MBJ/SBJ. When EGC's are landed on the Neutral bar of the main panel, ground fault currents on those EGC's do not pass through the MBJ/SBJ.
We need only to go to......
Hmmm. In 250.28(A), can the grounded conductor terminal strip be considered "similar suitable conductor" to a bus? I that think between Art. 100 definition of MBJ (for the EGCs) and the installation direction of 250.24(C) (for the disconnect enclosure) some rewording is due. I'll have to think about that one. If you are right, we need a lot more EGC bars in this world!
250.24 Grounding Service-Supplied Alternating-
Current Systems.
...
(B) Main Bonding Jumper. For a grounded system, an
unspliced main bonding jumper shall be used to connect the
equipment grounding conductor(s) and the servicedisconnect
enclosure to the grounded conductor within the
enclosure for each service disconnect in accordance with
250.28.
250.30 Grounding Separately Derived Alternating-Current Systems.
(A) Grounded Systems. A separately derived ac system
that is grounded shall comply with 250.30(A)(1) through
(A)(8). Except as otherwise permitted in this article, a
grounded conductor shall not be connected to normally
non-current-carrying metal parts of equipment, to equip-
ment grounding conductors, or be reconnected to ground on
the load side of the point of grounding of a separately
derived system.