Doesn't matter if the grounding bar is pre-install or furnished/bought as an add-in kit. Once installed per manufacturer's instructions, it is part of a listed assembly.We know that the grounding bar is not normally pre-installed by the manufacturer in a panel with a main breaker. We would have to define "unspliced" to settle on a connection from the grounded conductor to MBJ (screw or strap, for instance) to the enclosure to an EGC bar as being considered "unspliced".
There is no requirement which says the grounding bar must be directly connected to the MBJ. 250.24(B) only specifies that the unspliced MBJ connect the enclosure and the EGC's to the grounded conductor (and there is no stipulation the grounding conductor entering the enclosure be directly connected to the MBJ)
Absolutely correct.We know per 250.24(A)(4) that such a connection is not sufficient to allow the GEC to be connected there, it would need to be a wire or busbar.
I can, and I am... but only under "compliant" circumstances, and this would be based on the bonding screw being a means of connection (under 250.8) rather than the MBJ. Additionally, a terminal bar is also a connection means itemized under 250.8. So the terminal bar must be directly connected to the MBJ and not connected to the grounded conductor except through the MBJ. Note a jumper bus, such as used in many cases to bridge grounded conductor terminal bars on opposing side of a panel, is not one of the itemized connection means under 250.8. If it were to be dubbed the MBJ, the bar on one side could be used for EGC's while the bar on the other side could be used for grounded conductors.I am having trouble understanding this, I know you can't be accepting the grounded bar for the EGCs. In that instance, a section of the grounded bar is performing the Article 100 function of the MBJ, and the factory provided 'MBJ' (screw or strap) is bonding the enclosure. That section of the grounded bar is unspliced, even if hard to draw the dividing point on.
Now it is impossible to elaborate on each and every type of service panelboard here... so it comes down to evaluating each as it applies. And in that evaluation we must consider all the elements which must be in place to be compliant. Additionally we must keep in mind the concept behind each element...
IMO, the basal concept is to provide a star/single point connection for all grounded and grounding conductors... and we know that is impossible mechanically. In so much as separation is required, the concept is expanded upon so as to keep the separated connections of grounded conductors also separated from the separated connections of grounding conductors and bridge the two conglomerations by way of the MBJ.
Given that many service panelboard installers practice landing both EGC's and GNC's (grounded neutral conductors; not the brand name dietary supplements ) on the grounded conductor terminal bar(s) in semi-hap-hazard manner, I view that as an automatic violation of the expanded concept. However, I feel it will remain debatable as to its compliance.