The original thread was because the GFI on the generator was tripping, assuming the generator has GFI protection on the 30amp TL output...OK feeding a main breaker type load panel and a generator load panel that does not separate the grounds and neutrals the GFI senses the current flow through the bonding jumper ground loop thus created and trips. But why was the circuit breaker tripping? That happens when the generator connection cord or the generator inlet is wired improperly or an undiagnosed short down line. As I read it the generator has to be wired as a separately derived system if the ground and neutral are bonded in the standby power system. The short is a separate issue.
Sorry I don't mean to revive a dead thread but this was an interesting one. I have a question about this. This problem comes from the transfer switch being bonded to a bonded service panel which bonds the neutrals to earth right? Couldn't this problem be fixed by driving a ground rod by where the portable generator will be used in this application and connecting equipment ground to it. Wouldn't this stop the GFCI tripping issue and the GFCI would still trip from a ground fault..... since the GFCI is the first point of service entry it should be bonded there right and not at the transfer switch back to the load center? You would then just have to unbond the main panel Everytime there was a power outage correct? I'm trying to picture this in my head as most transfer switches I remember have their own neutrals and grounds and a load center with breakers but this I'm reading only switches hots and neutral is bonded.