I certainly can grasp it, I just disagree.
it's OK to be wrong :thumbsup:
I certainly can grasp it, I just disagree.
What's the difference? Also, we are using mathematical expressions to approximate what we see in the world. The voltages are not a 'consequence' of the math at this level of physics. It's the other way around.
I still don't think I received adequate responses to my post 241.
To me, if it was two phases, it would be two regardless of the reference point.
FIFY
The choice to earth the neutral and the choice to measure from only it are two different things.
We're not relying on the battery analogy when stating that if voltage L1-N can be derived from sin(x) then voltage L2-N can be derived from -sin(x).
What?
...
My problem is that it is not standard methodology at an applied electrical level.
...
And I'm not going to debate what is 'standard methodology' in the engineering field. My point is that for many day-to-day applications in electrical installation, polarity works just fine on these services when using phasor math would add time and money to a project. In fact, for resistive loads it produces the same mathematical resuslts. For waveforms where distortion matters I'm unconvinced it doesn't work better. Why is this so hard for some here to accept? I think you get it, just not sure about all others.
But different amplitudes. The 120-0-120 are in anti-phase, not the same phase. That's why the neutral current cancels, and that's the raison d'etre for this configuration.To me, if it was two phases, it would be two regardless of the reference point.
To me, if it was two phases, it would be two regardless of the reference point.
not sure you will ever be satisfied after 40 pages, so why try?
Totally accept all. I got no problem with alternative methods where parameters change.
You haven't been responding to that post for 40 pages. Give it a real try and maybe we'll find the common ground.
It doesn't matter if it is one coil with a center tap or two coils with a jumper. The coils consist of individual turns and the individual turns are electrically in series, and the center tap is simply connected to one of the turns (either directly or via the x2 x3 leads). They are equivalent.
It is a single phase transformer. Everyone here agrees that it is a single phase transformer. There is approximately a single flux coupling all of the turns of the coil (only approximately; remember leakage inductance). All of the turns of the coil develop approximately the same voltage.
That does not change the fact that there are _two_ apparent phase angles, that you can use these _two_ phase angles to do correct math describing the operation of the transformer and the neutral.
The _fact_ that you can do correct math to give correct predictions using phase angles of 0 and 180 is sufficient to make clear that the two phase angles are present. They are related by inversion, they are in some senses the same (zero cross at the same time), and by alternate selection of reference you can change the system to have only a phase angle of 0. But you can still do correct math with _two_ phase angles. We agree not to call the system a 'two phase' system, but clearly there are two phase angles available.
-Jon
Electrical theory governs. The sine wave L1-N and N-L2 are in phase, and if the correct math was applied, the same result would be achieved.
Electrical theory governs. The sine wave L1-N and N-L2 are in phase, and if the correct math was applied, the same result would be achieved.
:happysad:
earth is reference
at least in this inertial reference frame
Changes nothing. V1-n and V2-n are still in anti-phase.What if the neutral isn't grounded?