Full wave it is not. Full wave uses both half of the cycle. Half wave uses just the positive half. That's what hexaphase does.However, a six-rectifier 3ph supply could be called either six half-wave or three full-wave, which is what I meant.
Another way to look at it. A full wave bridge conducts through two semiconductors at the same time on each cycle. Half wave conducts through just one. The application normally determines which arrangement is most suitable. For high current, low voltage rectifiers half wave is often the better way to go. It doesn't make best use use of the transformer capability but the forward loss for the semiconductors is for one device at a time.
Also, back in history when semiconductors were expensive, half wave reduced the component count.