Mc bond wire

Status
Not open for further replies.

j rae

Senior Member
Has any body got mc hospital grade with a #12 alum. Bond wire? Very hard to twist around the jacket.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
You don't have to do anything with it, just cut it off.

Roger
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Sounds like you are using the new MCAP cable from Southwire.

I agree with Roger, just cut off the bond wire, there is no need to backwrap it.

Chris
 

j rae

Senior Member
Mc bond wire

Do you need to wrap the bond wire in mc around the jacket. This new mc i got has a #12 al. Wire makeing very hard to get in the connector. If so what code artical covers this?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Do you need to wrap the bond wire in mc around the jacket. This new mc i got has a #12 al. Wire makeing very hard to get in the connector. If so what code artical covers this?

110.3(B) requires you to install listed equipment in accordance with the listing instructions.

If you are using Southwires HCF MCap cable, then according to Southwires installation instructions you just cut the bond strip off where it emerges from the metal jacket. There is no need to backwrap or terminate the bond wire.

HERE is a link to Southwire and their Mcap cable.

Chris
 

iwire

Moderator
Staff member
Location
Massachusetts
I agree with the others and just want to add there is no requirement to back wrap the bonding wire on AC cable either.
 

Base7

New member
We were (last week) installing the bare conductor through to the ground screw and back out and wrapping the MC. The insulated ground was then dedicated to the receptacle. We were corrected this morning to cut-off the bare conductor at the end of the cable, and utilize the insualted ground to the ground screw and the outlet itself. This agrees with what you guys are saying, but it seems like we aren't satisfying 517 that indicates the isolated ground needs to be directly back to the grounding bar....
 

benaround

Senior Member
Location
Arizona
We were (last week) installing the bare conductor through to the ground screw and back out and wrapping the MC. The insulated ground was then dedicated to the receptacle. We were corrected this morning to cut-off the bare conductor at the end of the cable, and utilize the insualted ground to the ground screw and the outlet itself. This agrees with what you guys are saying, but it seems like we aren't satisfying 517 that indicates the isolated ground needs to be directly back to the grounding bar....

I think this is a redundant ground not an isolated ground.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
This agrees with what you guys are saying, but it seems like we aren't satisfying 517 that indicates the isolated ground needs to be directly back to the grounding bar....

What part of 517 are you refering to?

Roger
 
You guys have all got it wrong.

You bond the aluminum bond wire to the neutral bus. :roll: