Do you need to wrap the bond wire in mc around the jacket. This new mc i got has a #12 al. Wire makeing very hard to get in the connector. If so what code artical covers this?
Do you need to wrap the bond wire in mc around the jacket. This new mc i got has a #12 al. Wire makeing very hard to get in the connector. If so what code artical covers this?
Has any body got mc hospital grade with a #12 alum. Bond wire? Very hard to twist around the jacket.
We were (last week) installing the bare conductor through to the ground screw and back out and wrapping the MC. The insulated ground was then dedicated to the receptacle. We were corrected this morning to cut-off the bare conductor at the end of the cable, and utilize the insualted ground to the ground screw and the outlet itself. This agrees with what you guys are saying, but it seems like we aren't satisfying 517 that indicates the isolated ground needs to be directly back to the grounding bar....
This agrees with what you guys are saying, but it seems like we aren't satisfying 517 that indicates the isolated ground needs to be directly back to the grounding bar....