(d) Electric Light, Power, Class 1, Non–Power-Limited
Fire Alarm, and Medium-Power Network-Powered Broadband
Communications Circuits in Raceways, Compartments,
and Boxes. Communications conductors shall not be placed in
any raceway, compartment, outlet box, junction box, or similar
fitting with conductors of electric light, power, Class 1, non–
power-limited fire alarm, or medium-power network-powered
broadband communications circuits.
Exception No. 1: Where all of the conductors of electric
light, power, Class 1, non–power-limited fire alarm, and
medium-power network-powered broadband communications
circuits are separated from all of the conductors of
communications circuits by a permanent barrier or listeddivider.
Exception No. 2: Power conductors in outlet boxes, junction
boxes, or similar fittings or compartments where such
conductors are introduced solely for power supply to communications
equipment. The power circuit conductors shall
be routed within the enclosure to maintain a minimum of
6 mm (0.25 in.) separation from the communications circuit
conductors.
Exception No. 3: As permitted by 620.36.