Zero ohm?
Are you asking why the Armor Grounding Wire -- a specific designed product for working as GEC – needs additional bonding at both ends? Obviously if such product already meets the code, that it is already having the conduit bonded at both ends to the inside copper conductor, then it should meet the code. But in practice I would think many cases people buy a 30 ft armor wire and only use a fraction of the length for the job, meaning they cut the cable to length, which means the cut end needs to be bonded.
Here is a good article to explain the choking effect: http://www.ecmag.com/section/codes-standards/guardian-ground
“The magnetic field’s strength increases in proportion to the amount of current in the conductor. In many cases, the magnetic lines of force in the conductor are induced into the conduit enclosing the grounding electrode conductor; they can even surpass the saturation point of the steel raceway. At the point where the grounding electrode conductor exits the conduit, the magnetic lines of force generated by the fault current in the conductor will try to be induced on the end of the conduit, creating a saturation point that exceeds the conduit’s capacity. The steel conduit, in this instance, acts like a steel core of a coil to concentrate the magnetic lines of force. This condition is often referred to as the “choke effect” because it is actually the restriction of a grounding electrode conductor from performing its function. Because of this, specific bonding requirements are necessary for ferrous metal raceways that contain grounding electrode conductors. This is not a concern for grounding electrode conductors that are installed in PVC conduit or other nonferrous metal raceways such as aluminum or brass conduit.”
Respectfully, you are missing the point. Armored grounding wire is NOT a bare copper conductor inside a raceway (conduit).
And the listing, as KDER - Grounding and Bonding Equipment, puts it outside of Armored Cable or Metalclad Cable. So I doubt that it is even a cable.
The Code is silent about bonding the armor of Armored Grounding Wire to the wire contained in the armor.
What do you think the name “cable armor” below means?
A factory assembly of two or more conductors having an overall covering.
I don't think it means KDER -- Grounding and Bonding Equipment.
Then what do you think what else the article was talking, if not Grounding and Bonding Equipment?
Come on, we were discussing about the rule of bonding GEC ferrous enclosure, not the definition of cable armor.
I wanted to say that the name "cable armor" in the article and your "Armor grounding wire" are interchangeable, they refer to the same device.
My point is that even if a legitimate Armor Grounding Wire was used for GEC, and only the bare copper wire was clamped to the grounding electrode, then it is a violation.
Only when the steel armor and the copper wire were clamped together at both ends – bonding the armor to the copper wire – then this is compliant.
NEC says:
1) Armor grounding Wire: the steel armor must be bonded to the copper wire at both ends
I agreed that the article is better off using the standard terminology, i.e Armor grounding wire instead of cable armor in the context, for less confusing.
A picture is worth a thousand words.
http://www.mvpllc.org/mvp99.html
Why people went through the trouble of making this clamp and bonding the steel armor to the conductor if not needed?
A picture is worth a thousand words.
http://www.mvpllc.org/mvp99.html
Why people went through the trouble of making this clamp and bonding the steel armor to the conductor if not needed?
1)
http://www.ospmag.com/issue/article/032012-McCarty
From NEC 2011, 250.64 Grounding Electrode Conductor Installation.
“ it shall be protected in rigid metal conduit (RMC), intermediate metal conduit, (IMC) rigid polyvinyl conduit (PVC), reinforced thermosetting resin conduit (RTRC), electrical metallic tubing (EMT), or cable armor.”
2)
https://www.mikeholt.com/videodisplaynew.php?pageid=4139
(E) Enclosures for Grounding Electrode Conductor. Ferrous (iron/steel) raceways, boxes, and enclosures containing the grounding electrode conductors must have each end of the ferrous metal raceway, box, and enclosure bonded to the grounding electrode conductor [250.92(A)(3)]. Figure 250.115
From (1) I interpret cable armor as an enclosure for GEC.
And (2) says it must have each end bonded to the GEC.
Enough to satisfy everyone? For me I think this is more than enough to say that Al's Armored Grounding Wire must have each end of the armor bonded to GEC, unless Al can show that said armored grounding wire assembled at the factory already having each end of the steel armor bonded to the inside conductor.
11. No need for Armor removal from the wire.