But this makes me wonder, is an MC connector connected to a metal box which is grounded an approved method for bonding?

Yes, an MC connector is listed for grounding.

The outer armor of MC is required to be grounded just like any metal raceway or metal enclosure.This is regardless of the fact there is a green EGC inside the MC.
 
mc in plastic boxes

P.D. must be pullin' our legs to see how long this can go on!
There are acceptable methods allowing a transition from one cable/wireing method to another-that would easily be NEC compliant and make sense.
If you attempt to try a silly method-and I do mean MC into plastic is pretty silly other than as an academic exercise-I'd say you stand a good chance of being EASILY shot down-and wether you like it or not the easy way to squash an argument like this will involve the infamous "Listing" requirements of everything involved in this hypothetical --and I hope that is all it stays as -situation.
If comon sense and what we know can work was all it took -well then mad max installations would be beautiful-but we do have to follow the rules-even when we might think we know better--
I've seen people try to stick a piece of mc into 1 side of a plastic nail on and tie into a piece of RX coming out of the same nail-on--
AND THEY SOLVE THE DILEMA BY CUTTING AWAY ALL THE GROUNDS!!!!
It's been a rough day-Find a wire manufacturer who'll go along with this,a connector manufacturer who'll go along with this,a wire nut ...etc... and maybe you'll be able to do it the way you describe.
You won't be able to get them to say its ok because their lawyers will not allow it-no matter if you think you know better.
 
P.D. must be pullin' our legs to see how long this can go on!

Not at all. Show me the code(s) that say it can't be done. And yes, this is an "academic exercise" to get people to actually see what the code says and apply it correctly, rather than just blindly following some mantra like "That doesn't seem right to me" or "It can't possibly be legal" etc etc.
 
110.3(b) it is not installed in accorrdance with it's listing(Talking about the box that Marc had posted)
 
I'm thinking that the only way to connect to the box Bob posted is with a junction box adapter and by that I don't mean a terminal adaptor ,.. seems I looked into this and terminal adaptors are for threaded hubs and metal boxes ,..I highly doubt that listed M.C. connectors would be listed for connection to a PVC junction box. I'll see what I can find:roll:
 
Well ... I did not find anything that says MC connectors are limited to metal boxes nor did I see a limitation to their use in K.Os ,.. so if ,.. and I doubt there would be , given the thickness of the type of box Bob posted,.. there were enough threads left for a bonding bushing ,..The language does allow for it ....
 
.. so if ,.. and I doubt there would be , given the thickness of the type of box Bob posted,.. there were enough threads left for a bonding bushing ,....

Leave the locknut out of the equation.


That said, it is not something I have run into more then one or two times. :smile:
 