peter d
Senior Member
- Location
- New England
Still no reply from bridgeport now why doesnt that surprise me. Typical new england.
You're more than welcome to stay on Long Island.
Still no reply from bridgeport now why doesnt that surprise me. Typical new england.
And that is certainly false statement by Carlon.
Here is a PVC box covered by 314.3, it happens to be a cantex.
Is adding a KO to this box a UL violation?
Or was the above box manufactured not to be used?
Or are the rules different for smaller boxes and if so where is that explained?
314.3 applies to all non-metallic boxes not just single gang device boxes. :smile:
You could always use the Carlon box adaptors that pass through the box wall from the inside and glue into a coupling.The pvc in that box is probabbly 1/4 " thick making it difficult to find a connector that has threads long enough to reach the other side of the connector.
I beleive you have to use a grounding bushing if you use mc in a plastic box, and then try to wrap the wire around point of connection
Why ground a plastic box?
You have to bond the armor of the MC cable somehow if you happen to terminate it in a plastic enclosure.
Yeah I thought of that. But then I realized they must have it bonded on the other end.:smile:
What are you doing up so late any how?
http://database.ul.com/cgi-bin/XYV/...n=versionless&parent_id=1073991695&sequence=1SINGLE-GANG BOX
A box nominally 2-1/4 by 4 in. or smaller is intended for one or more nonmetallic sheathed cables to enter through a single or multiple stage knockout opening.
why? the armor isn't a ground.You have to bond the armor of the MC cable somehow if you happen to terminate it in a plastic enclosure.
why? the armor isn't a ground.
seems kind of overkillBecause the armor is metallic and must be bonded. It makes no difference that it isn't a "ground." It has to be bonded for the same reason we have to bond all metallic non-current carrying parts.
seems kind of overkill
well yeah. Alot of things in the code are overkill.Following the code is overkill? It only had to be bonded once at one end of the other, but it still has to be bonded.
well yeah. Alot of things in the code are overkill.
I've never used MC in Plastic boxes for one. But if I ever did I would imagine that the other end would be connected in a metal box therefore being bonded at the other end. But this makes me wonder, is an MC connector connected to a metal box which is grounded an approved method for bonding?Well, this is not one of them. So you're suggesting it's ok to leave a metallic part of a wiring method unbonded? Especially something like the jacket of MC cable which could easily become energized?