cschmid
Senior Member
- Location
- Northern cold country
If you are looking for an inexpensive way to test the 25 ohms to ground there is a method used for approving the grounding plate of a generator setup at a portable pit for road construction. I cannot find the info so if anyone has it would be good to know. It uses a battery and two rods and some other stuff. The downfall is it takes about an hour or so to do. The best way is a ground resistance tester takes minutes to do. But I find the discussion about whether one or two rods will make a difference interesting. When the IEEE has determined that a rod less than 10ft in length will not provide 25 ohms or less to ground on a continual basis due to a variety of weather condition and soil conditions. So if you are actually looking for effective grounding you need to use screw together rods and go deeper into the earth. This is a link to just one of the papers produced in this debate. http://www.cpccorp.com/deep.htm The findings of the IEEE is why the NEC has required us to use the rebar in the cement foundation. So I don?t really believe in the 2 rod issue yet every inspector requires it if you do not have a foundation (grid) ground. I believe that rebar in a foundation equals a grid. So if 25 ohms to ground is an issue use screw together rods and go deeper.