Microwaves

Status
Not open for further replies.
I have seen some that say a 15 amp circuit. Many don't require an individual circuit but recommend it. If the mw is a countertop then the NEC will not be affected as the small appliance branch circuit will handle it unless one decides to run a circuit. In that case it must be a 20 amp circuit but if it is built in as a range hood then it may not necessarily require a 20 amp circuit

As far as I was concerned this was a mythical microwave and we were discussing codes.
 
It's going to be tough wrapping those #10's around the receptacle screws. Besides they're not designed for that.

We have to do that all the time and I pretty sure all devices are required to accept 10 AWG on the screws.

I think the only recs that are not listed to accept 10 are the cheapos. Pretty much all of the Spec grade or better is- and its easier to just use the plates on those for that thick wire.
 
We have to do that all the time and I pretty sure all devices are required to accept 10 AWG on the screws.
It's not fun with #12, I can't imagine having fun with #10's not to mention stuffing the wires into a 1 g box
 
I think the only recs that are not listed to accept 10 are the cheapos. Pretty much all of the Spec grade or better is- and its easier to just use the plates on those for that thick wire.
You're right. I forgot about the pressure plate commercial grade ones.
 
It's not fun with #12, I can't imagine having fun with #10's not to mention stuffing the wires into a 1 g box

:D

Tell me about it, we might have 5 solid 10 AWGs on a duplex, however there will be a 4" sq deep box with a single gang plaster ring on it for the room.
 
:D

Tell me about it, we might have 5 solid 10 AWGs on a duplex, however there will be a 4" sq deep box with a single gang plaster ring on it for the room.

No way I'm putting that many #10's on a receptacle, that thing is getting pigtailed with wago's. :happyyes:
 
Not only that, a cheap resi grade duplex will probably break trying to stuff it in.
Again, not thinking out of the box, I assumed in this thread that we were talking about residential work. I probably wouldn't come prepared with a 20A commercial grade receptacle if I were doing a residential kitchen
 
It's going to be tough wrapping those #10's around the receptacle screws. Besides they're not designed for that. Let's all be clear, we're talking about std., fixed in place microwaves. Any other types that require special wiring you will need to know the specs up front during the rough. I agree, you are not required to install a 20A circuit but again, if you have some $$ in the job I would run #12

Unless the run is over 125 feet, why would you?
 
Yes, for a counter top. An over the range will do fine on a 15 amp circuit.
Yes, but the point is only if it is a non-SABC receptacle. It is dependent on the receptacle/circuit classification as well as the microwave type.
 
Then #14 is sufficient :thumbsup:
If we're running a 15A circuit to a cabinet for an above range microwave unit, does the receptacle have to be a single or can it be a duplex ? Singles are generally a bit more $$ but I don't carry them on the truck. If a single is required is it acceptable to snap off the tab on the hot side and,in effect, make it a single ?
 
How many of you guys are seeing residential microwaves with 20 amp plugs on them? I have not seen any.

If they have a 15 amp plug a 15 amp circuit is not risky.

That said, if it is in a kitchen I agree with smart$ it needs to be 20.

hmmm, what about a 1875 watt hair dryer that uses the non-20A cord cap? this wattage exceeds 15A bc rating so it would need a 20A ckt. just because the device has non-20A cord cap does not mean a 15A bc will suffice.

If we're running a 15A circuit to a cabinet for an above range microwave unit, does the receptacle have to be a single or can it be a duplex ? Singles are generally a bit more $$ but I don't carry them on the truck. If a single is required is it acceptable to snap off the tab on the hot side and,in effect, make it a single ?
i believe you look at the yoke. if it carries one recept then thats a single. more than one on the yoke then its not a single.
 