electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
What size are the conductors? Sounds like a pretty easy task to pull them out and back in with a small neutral.
Sorry space out...I didn't get much sleep last night. Was thinking of an instrument meter socket not self contained, even though I said self containedSo sounds like this is a 11 jaw self contained meter? I wonder if they would allow a small 1:1 transformer delta ->wye transformer for the 4 voltage terminals?
Two sets of three 500kcmil in separate UG PVC conduits over 100' long installed 50 or more years ago.What size are the conductors? Sounds like a pretty easy task to pull them out and back in with a small neutral.
That brings up another couple of questions. We are allowed to reduce the neutral to the size of a bonding jumper per 250.102 but that table directs us to size it at 2/0 because the two 500's sum to between 600 and 1100. Can we split that in half and run two #2's, one per conduit? I assume that we cannot run a neutral in just one of the conduits; is that correct? It doesn't seem reasonable to me that we would have to run a 2/0 neutral in both conduits.
Funny, just yesterday I pulled 2 100' runs of 500-500-500-4/0-2/0 AL. You must be super jelly of my 4/0 neutral.Two sets of three 500kcmil in separate UG PVC conduits over 100' long installed 50 or more years ago.
That makes no sense to me. The CCCs are split, why not the neutral? It's not like an ECG that needs to be able to clear the fault for the whole rating of the OCPD.According to 250.122(F)(1)(b), it seems like you'd have to run a 2/0 in each conduit.
I'm wondering if there's some sort of overcurrent protection inside of the meter that allows a #14 neutral wire to be used. I don't think that would affect what you have to use for the neutral conductor on the feeder, but it is kind of a crazy situation.The connection to the neutral in the PV meter is just a short piece of #14. I would have thought (hoped) there existed a small transformer I could connect to the phase conductors that would tell the meter where the center of the wye is, but that's just my fantasy.
That's something I hadn't thought of: an isolation transformer that only derives the neutral. I wonder how small such a transformer I can find. I wouldn't even have to worry about what the secondary voltage is, would I?The wye side of a delta:wye transformer can be used to derive a neutral. Nothing gets connected to the delta side; your three phases are connected to the wye, and X0 becomes your derived neutral.
I would think so, but there's still the issue of the minimum sized neutral being tied to T250.102(C)(1) which makes no provision for splitting it for parallel sets. The table is meant for grounding jumpers which cannot be split like that.Would 310.10(G)(1) Exception No. 2 : possibly being utilize, under this particular situation (?)
..Curious..
There is no neutral load, really; it's just for instrumentation.IMHO you would size it and treat it just like the zig-zag. It would only need to supply the expected neutral load....if you were allowed to use it at all.
Don't think of it as an isolation transformer so much as an autotransformer that just happens to have an isolated coil inside the box. You are only connecting to the wye coils.
Jon
I believe there's still the issue of 215.11 that Wayne raised earlier.
I know I could do it with a delta-wye isolation transformer, or trenching over 100' to the disco, or pulling a neutral through 100'+ of ancient underground conduit, but I am looking for something easier and cheaper.
It should create a neutral that is normally in close proximity to same voltage as the source neutral, but you probably do not want to ground it or you can possibly have unwanted current flowing on unwanted paths. And if OP ran a grounding conductor back to the service, he would no longer need the autotransformer. You should only ground at the service or at separately derived systems.I think either a zig-zag or a "wye grounded delta" (the one I was mentioning) would be considered as an autotransformer because it does not produce an output that is isolated from the input.
In the application being considered by ggunn, it would not really be a "grounding autotransformer" as in 450.5 because it is not "providing a neutral point for grounding purposes", even though it is providing a neutral.
I agree, though, that 215.11 could be problematical in this case.