For 120/208-240 feeders probably not bad idea. For 480 volts - I seen many feeders with no neutral as all that was supplied was 480 volt loads. Not much for common 277 volt loads other than lighting to potentially be added where 120 volt loads of many kinds are pretty common.This is why I ussually suggest running a neutral even if planned loads will not require one, eventually soneone wants to add something that does.
OP, is conduit large enough to pull in a neutral? Might be easier than trying some creative way to sidestep the required neutral. In this circumstance I see this particular meter as just another device requiring a neutral. Is there a different meter not requiring a neutral?