101002-1707 EST
tallgirl:
Why does this CAT-5 cable have to go in anything?
Because the client already rocked in the walls and I'm not in the mood to drill holes in anything to run it any other way.  Also, it has to penetrate the roof somehow, and dittos for not being interested in penetrating the roof.
I sold one of their clients an older version of my monitoring gear and tried to up-sell them on more instrumentation.  They countered with "we'll pay as much as we paid last time", which is sort of okay because I need a reference system.  The goal was to get in and out for as little of my time and energy as possible.  If their electrician can pull the sensors wires, and I just supply the cable, I get out cheap.
			For analog signals of the low data rate and reasonable voltage levels that you mentioned I do not see a noise problem with twisted pair wires.
There is no "data rate".  The device that performs the measurement provides 5VDC (and ground) and the sensor returns a voltage that is proportionate to the temperature.  The return voltage is sampled every 5 or 6 seconds and then used to perform temperature correction on the array's expected output.  See this page --
http://data.digitalgnomon.com:8080/?port=3&array=y
That's my array, though it is more "lab install" than "finished install".  At some point I'll have to put pipe on the roof so I can put all those sensors AT the array.  Need to reconfigure the array as well or else cut down a neighbor's tree ...
			If you are interested in a different temperature measuring means, then some products I am working on that use Dallas 1-wire devices might be of interest.
I've looked at 1-wire and the issue I have is converting the 1-wire data into something the device that does the monitoring can read.  Yes, 1-wire is a technically better solution, but the problem with 1-wire is reading it with the hardware that I have.  Some day when my company has more money to invest in hardware development I might go that route.  Or as I like to say, "Do you have $50K you're not using?"  If any of y'all would like to invest in a company that can monitor the heck out of a commercial solar power plant, let me know.  I use off-the-shelf parts, so my prices are lower than all of my competitors, and I'm very clever with software, so I'm able to add products much faster.
			Some questions on your Hourly Data Plot.
What does Inverter KWH mean? Is this the output power (energy) from the inverter?
What does Charger KWH mean?
Is this a grid-tied system?
Power usage seems to have a strange profile. Why is there very little usage above the base level?
Inverter KWh is power from the inverters.  Inverter output in excess of load is "sold" to the grid.
Charger KWh is DC output from the charge controllers to what is essentially the system's DC buss.  The difference is conversion loss as well as battery "float loss".  There are 25KWh of batteries at 48 nominal volts being floated and that can add up.
It's a "Hybrid" system -- works like a "Grid-Tie" system while the grid is present and an "Off-Grid" system while the grid is gone.  The inverter outputs go directly to the main 60A sub-panel that feeds the interior of the house.  The inverter inputs are bidirectional and backfeed the 125A service panel when "selling" and are fed when "buying".
The power profile looks like it does because my average load is a fraction of yours because I'm very good at greatly reducing electric consumption (and I sell this as a service with a money-back guarantee).  The other reason is that the inverters only power interior loads, not the A/C compressor outside.  So "Inverter KWh" ignores the A/C compressor.  Not that it matters -- the loads really are extremely low.  My "net" consumption is about 7,000KWh over the past 21 months.
			Note: Since you use KWH at one hour sample points I can also read the graph as average KW without a scaling factor.
Yes, I'm very clever that way :grin:  Do you like the way it changes each time you refresh the page?
			This is a quite different from the profile for my home. Overnight I have about 0.75 KW and 1.5 to 3 KW average levels thru the day and evening.
That's because you likely waste a lot of electricity.  And I don't mean that in an insulting way -- most people waste electricity for no good reason because they don't have their homes instrumented at all.  I have a distributor (I sell solar power monitoring stuff internationally and consult with firms here in the US, Canada and parts of Europe) in South Africa who is making a killing reselling electric power monitoring devices.  The pay-back period on something like an Envi or TED 5000 is usually measured in weeks to months.  I sell "
Kill-A-Watts" from a web page and people run around figuring out what is wasting power and what isn't.
I think I'd have to turn all kinds of things I don't need on to get to 3KW.  My peak demand load, according to the PoCo's meter, is 5.5KW.  And I live in Central Texas, have A/C, an electric motorcycle that needs charging, and typically have 4 or 5 computers, including a server running 24/7, along with two WAPs, cable TeeVee, several wide screen televisions, etc.
The key is actually using the electricity you buy, and not just buying electricity.  A lot of people buy electricity they never use.