Multi ground wire splice

Status
Not open for further replies.

bluecollar84

Senior Member
Location
US
I have a pvc box with 6-8 #12 ground thhn wires that I need to splice what's the best way to do this. Also this jbox is outdoors


Sent from my iPhone using Tapatalk
 
There is no twist-on connector listed for 8 #12 so your best best is to use a small ground bar kit. It's definitely better than trying to splice that many wires under a twist-on connector anyway, even if you could do it.
 
I have a pvc box with 6-8 #12 ground thhn wires that I need to splice what's the best way to do this. Also this jbox is outdoors


Sent from my iPhone using Tapatalk

I agree w/ Peter d about a bar.

But if you insist on using wire nuts, you could use a couple of the Dryconn blues with a jumper between them (IIRC those max out at 4 or 5 #12s per unit).
 
Last edited:
There is no twist-on connector listed for 8 #12 so your best bet is to use a small ground bar kit. It's definitely better than trying to splice that many wires under a twist-on connector anyway, even if you could do it.

That or an 8 port WAGO:

https://www.amazon.com/478047-773-168-Push-Connector-Conductor/dp/B00HRHXMTU

afaik, the largest wire nut is rated for 5 #12s. Some are rated for 5 #10s, tho there is no translation for if or how many #12s it could hold.
 
I would go with the 2-5 wire splices jumpered together. Just use the correct wire nuts.
 
I have a pvc box with 6-8 #12 ground thhn wires that I need to splice what's the best way to do this. Also this jbox is outdoors


Sent from my iPhone using Tapatalk

There are all kinds of options.

Wire nuts and terminal strips are probably the simplest.

Wire nuts are probably the fastest solution.

https://www.automationdirect.com/ad...N-Rail_Terminal_Blocks/Ground_Terminal_Blocks

These are $2-3 each. I think you can get two wires on each side so you would only need two of them and a small piece of DIN rail to mount them on.
 
Actually, I never gave it a thought. Are wire nuts suitable for outdoor connections?

I believe only those listed for it, such as DryConn.

I don't think the WAGO are, just wondering if anyone can enlighten with specific info.

Looking for something better than a Buchanan splice filled with Noalox, which isn't listed but which I personally trust a whole lot more than a wirenut with slippery goop inside.
 
Are those WAGO connectors suitable for outdoor locations?
Even twist on connectors probably have similar rating. I have been looking a little but found nothing yet on WAGO site, but wonder if one doesn't need to look in the UL white book.

I would guess either is rated for use in wet/damp location enclosures, but not in submersible applications.
 