Minimum Circuit Ampacity
44.14 The minimum circuit ampacity (MCA) required by Clause 44.3(h) shall be determined as follows. All concurrent load conditions shall be considered in the determinations; see Figure 44.1. Whichever load condition provides the highest value shall be used.
a) For a motor group only, a load consisting of two or more motors, the rated current of the largest motor or branch circuit selection current, if marked (see Clauses 44.11 and 44.12), or the MOC and MRC required by item (f) of 44.3, multiplied by 125 per cent, added to the rated currents of all of the other motors.
b) For a combination load, a load consisting of one or more motors, electric heaters, and any olher loads, that incorporates one or more compressor motors, the rated current of the largest motor or branch circuit selection current, if marked (see Clauses 44.11 and 44.12), or the MOC and MRC required by item (f) of 44.3, multiplied by 125 per cent, added to which shall be the value obtained by multiplying the rated current of the electric heaters by 125 per cent, and adding to that total the sum of the ratings of all other loads.
c) For a combination load, a load consisting of one or more motors, electric heaters, and any other loads, not involving a hermetic refrigerant motor compressor, the sum of the rated currents multiplied by 125 per cent.