Large dairy with circulating fans originally installed about 20 years ago.
Fans are 1/2 hp 480v with internal thermal protection. About 15 to 20 fans per branch circuit protected via an AB1489 mini 30 amp CB. #12 AWG. They were all started with single motor starter.
Trying to determine if it was ever a legal install.
I do not see it passing 430.53 (B). Table 430.52. NEC 2014, but what about years ago?
Fans are 1/2 hp 480v with internal thermal protection. About 15 to 20 fans per branch circuit protected via an AB1489 mini 30 amp CB. #12 AWG. They were all started with single motor starter.
Trying to determine if it was ever a legal install.
I do not see it passing 430.53 (B). Table 430.52. NEC 2014, but what about years ago?