resistance
- WA
Exactly!A cabinet can be used as a raceway but is not necessarily a raceway.
It is a raceway when it's used as a raceway as is the case here.A cabinet can be used as a raceway but is not necessarily a raceway.
Seems you are saying the samethingIt is a raceway when it's used as a raceway as is the case here.
Roger
Yes I am, just didn't want there to be any doubt.Seems you are saying the samething![]()
Well for the sake of the matter, let's look at the pertinent text...Yes I am, just didn't want there to be any doubt.
Roger
230.7 Other Conductors in Raceway or Cable. Conductors other than service conductors shall not be installed in the same service raceway or service cable.
312.8 Enclosures for Switches or Overcurrent Devices. Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.
And if the problem conductors terminated on this disconnecting means instead of passing through there would be no issue.A panelboard containing the service disconnecting means is not dedicated solely to being a service raceway.
I agree with you. I don't like the installation but can't find any section that prohibits it either.Well for the sake of the matter, let's look at the pertinent text...
230.7 explicitly states other conductors in same "service raceway or service cable". This indicates to me that the explicit purpose of the raceway or cable is to contain service conductor. A panelboard containing the service disconnecting means is not dedicated solely to being a service raceway.
312.8 is about maintaining adequate space for conductors pertinent to the enclosure... not that you absolutely can't use the enclosure for feeding [service?] conductors through it.
...and I would agree :huh:And if the problem conductors terminated on this disconnecting means instead of passing through there would be no issue.
Roger