LarryFine
- Henrico County, VA
- Electrical Contractor
In my opinion, if exceptions apply in the field, they should apply when testing to qualify to work in the field.
So do I but that won't get you, me, or anybody else a passing grade if the test doesn't see it our way.In my opinion, if exceptions apply in the field, they should apply when testing to qualify to work in the field.
I remember in Tom Henry's exam prep he points this out in the preface I believe.I always did poorly on exams because I would mess with the exceptions. I wish I had talked to Smart$ earlier in my life...hahaha
I agree, it should say "without exception" if they do not want you to include the exceptions. The exceptions are part of the code just like the main rule.To me this question as written is flawed as it does not indicate whether you should include the exceptions. In licensing exams these types of questions lead to exam challenges. It should have indicated whether you are to consider Exceptions.
I skimmed through that and it refers to rounding as in 220.5(B), but I did not see any mention regarding exceptions. They do provide an email specifically for corrections or comments about questions. I may just use that email to contact them. A picture of the book is below.Does Mike include any advice in the preface or introduction?
Roger
I don't like that approach, it is tricky.It would be with the exception but you didn't say if the exception was part of the testing or instructions for the testing.
Roger
Then IMO you should contest every question you got wrong that has an exception.What if the exceptions are not addressed at all?
Mike Holt said:For a question to have an exception apply, the question must include the text of the exception. For the exception to app, you are required to have a two-pole breaker, not two single-pole breakers with a handle tie. This is because two single-pole breakers with handle tie does not ensure that the two poles will open simultaneously.