- Connecticut
- Engineer
Are we talking hardware or theory here?
Larry, we are talking hardware AND theory here. It is the same. If you remove the neutral from the circuit, you have a different circuit both in the physical world and theoretical world.
No, it's not. I'm talking about the circuit with the neutral connection broken. As long as the loads are balanced, the voltage between source-N and load-N will be zero even with no neutral.
Larry, you start out disagreeing with me here, but end up stating the same thing that I did. The is no potential difference from N load to N transformer (with an ideal circuit) regardless of whether the neutral is connected or broken, whether the loads are balanced or not. As you state, the voltage between source-N and load-N will be zero.
That's because you're using imbalanced loads. We weren't.
You are missing the point of that example. It was put forth by someone that there has to be a potential difference from source-n to neutral-n in order for current to flow in the neutral. In that example, there is clearly NOT a potential difference from source-n to neutral-n, but there IS current flowing in the neutral.
Note that both equations express zero neutral current, which has been our point: One circuit behaves just like the other one: no current between the source neutral and the load neutral.
Of course, the two circuits are physically different. The point is to show why no real current flows in the neutral. Not just no mathematical or theoretical current, but no real current.
Yes, both equations express zero neutral current. That has been my point as well. Of course no "real" current flows in the neutral, just as the mathematical or theoretical current will be zero. The point is that just because one circuit "behaves" like the other does not make them the same circuit. My original point is that the neutral has not been bypassed, it is still an active part of the circuit. Nor is there no current flowing in the neutral because there is "no potential difference along the neutral in a balanced circuit" as has been suggested. It just happens that there is zero current flowing on it. That is not the same as an open circuit at the neutral.
Correct me if I'm wrong, but doesn't all of that say "zero neutral current?"
Yes, it does. That's what I've said all along. I guess the only place we disagree is in your post #119 where you say that if there is zero voltage difference between two points, a conductor between them will carry no current. My earlier example of a 12 volt battery with a 12 ohm resistor connected by a zero impedance (ideal) conductor shows that there will be no voltage difference between the battery terminal and resistor terminal, but current will obviously be flowing through that conductor.