Is the source of the noise the conductors vibrating in the conduit or the conduit vibrating in its supports?
I would say the source of the noise is the vibrating conductors but it is amplified by the conduit vibrating in its supports. Qualitatively, you can feel the conductors at the ends of the conduit vibrating much moreso than the conduit itself. However it seems very interesting that the fields I am measuring with the Guass meter are much stronger along the conduit than along the exposed conductor at either end.
I should have mentioned by now, the electrician acknowledged late this week that he wished he'd gone with supports on every steel building frame member at 6 ft centers rather than skipping every other one and going 12 feet. I guess the code says every 10 feet so he knows this is insufficient and is probably going to add more supports but that work is not scheduled yet.
Even if that does dampen the vibration, I still don't think it will get us to the root cause. I'm still trying to answer the question, are fields of the magnitude I am measuring along the entire length of conductors normal in this type of installation?