You're not reading 310.10(H) correctly. Look specifically at (1). No EGC's on that list.
(H)(5) EGC
I don't know what else to say, it says right there in bold what conductors are permitted to be paralleled. NO EGC's.
(H) Conductors in Parallel.
(1) General. Aluminum, copper-clad aluminum, or copper
conductors, for each phase, polarity, neutral, or grounded
circuit shall be permitted to be connected in parallel (elec-
trically joined at both ends) only in sizes 1/0 AWG and
larger where installed in accordance with 310.10(H)(2)
through (H)(6).