No doubt short circuits are being re-labelled arc faults that just dont happen to trip a breaker magnetically.
Its openly admitted a series arc fault is 100 amps and over. Even if this is a peak value, the RMS equivalent would still be way over the trip curve of a 15 or 20amp breaker. I cant see a short lasting a few seconds tops as apposed to a few cycles setting wood ablaze. I can hold a lighter (which I have out of experimental curiosity) for a few seconds to a 2x4 and while it does leave a local char it does not set the wood a blaze. This of course is assuming an over driven staple. Such a worse case short circuit inside a box would have no effect to begin with.