FionaZuppa
Senior Member
- Location
- AZ
- Occupation
- Part Time Electrician (semi retired, old) - EE retired.
can you check my math. the calculated temps are above 90C. this scenario seems like a hazard (if my math is right).
note: it's open air calcs with no consideration for heat loss. in real world some of the heat would leak out and final temp would be slightly less, but not that much less.
note: it's open air calcs with no consideration for heat loss. in real world some of the heat would leak out and final temp would be slightly less, but not that much less.
Code:
[SIZE=1]per Eaton spec 1pole 10-70A breakers
1min-3max sec trip @ 104F (40C) to trip rated 40A @ 750% (120v/0.4=300A)
using 3sec case (75ft of #14 NM, two CCC's)
1W = 1J/s
300^2 * 0.4 = 36kW = 36kJ/s
36kJ/s * 3s = 108kJ(total)
energy per ft
108kJ/150ft = 0.72kJ/ft
copper heat capacity (noting that copper wire is an alloy)
3.45 J / (cm^3 K)
#14 0.0641" dia = 0.16025cm
1ft(volume) = 0.080125^2cm * 3.14 * 30cm = 0.6048cm^3
2.08656J/K * 1/0.72kJ = 0.002898/k = ~+345K = +161F
temp of wire = 104 + 161 = ~265F
if my math is right, the copper (150ft, 75ft #14NM two CCC's) would get up to ~265F during a 300A short for 3s.
**********************************************
per Eaton spec 1pole 10-70A breakers
3min-11max sec trip @ 104F (40C) to trip rated 40A @ 375% (150A)
using 11sec case (150ft of #14 NM, two CCC's)
1W = 1J/s
150^2 * 0.8 = 18kW = 18kJ/s
18kJ/s * 11s = 198kJ(total)
energy per ft
198kJ/300ft = 0.66kJ/ft
copper heat capacity (noting that copper wire is an alloy)
3.45 J / (cm^3 K)
#14 0.0641" dia = 0.16025cm
1ft(volume) = 0.080125^2cm * 3.14 * 30cm = 0.6048cm^3
2.08656J/K * 1/0.66kJ = 0.00316/k = ~+316K = +109F
temp of wire = 104 + 109 = ~213F
if my math is right, the copper (300ft, 150ft #14NM two CCC's) would get up to ~213F during a 150A short for 11s.[/SIZE]