FionaZuppa
Senior Member
- Location
- AZ
- Occupation
- Part Time Electrician (semi retired, old) - EE retired.
IMO, I think you should also run 1 sample in open air, just to get an idea of where the ampacity tables stand. Do they lean toward open air or worse case?
i have issue with such test. the table (pdf) you posted a few posts back, that says "amps at failure". basically thats a test to show how many amps can flow in open air @the specific ambient before insulation failure. i think they called it "melting". their definition of "melting" is not clearly defined.
i will run an open air test but not looking for a failure point, will simply be taking temp vs amps measurements. the UL tests wire is tested under has better defined test verbiage, meaning, the specific UL test for "pass" or "fail" has better defined limits.
if i test the wire and i see 25A @ 78C, this alone is not accurate enough to say it is safe or it is not safe. if @20A the insulation is all gooey and starting to pull away from the copper, even if temp is say 67C, that would be bad, and on flip side, if @26A i see 89C but the insulation is still perfect, this is better, but the temps may be posing the issue to its surroundings.
so just to be clear, i am only measuring temp vs amps in what NEC might consider worse case scenario for NM-B.