romex jockey
- Vermont
- electrician
feel free to argue this.
Would you happen to know the # to copperholics anonymous ....?
~R
~RJ~
Grand Q's FZ
I'm compelled to ask how the nrtl's asses ? there should be some data we can place side by sided to your findings ...~RJ~
dunno, what lab(s) has tested any of this before and have the osha cert? certainly my garage doesnt fit the bill, but the data i am providing is pretty darn accurate as far as i can tell. whatever discrepancies start to show up simply means we need a lab like Argonne (or university) to do formal testing.
and sure, the insulation on the wire started to cool before i tried to knife it, but before i started the video i did try to peel it right when it came out of the oven, wasnt very soft. again, just some crude testing looking for obvious failures, none found, now getting ready to cook (with amps) the romex in a R10 rigid foam sandwich.
So what's the dif between 'oven' and 'amps' doing the heating here FZ? All i can think of is 'external' / 'internal' .......?
~RJ~
amps = not cooking it in my gas oven
does anyone have the actual UL 2556 doc? if not i can accept donations to buy it, only $716.![]()
Unfortunately thats how they make $$$$, making standards, copyrighting them and then selling them.
more data for you. baked @300F for 90min.
the outer sheath got a tad like a rubber-band, it started to stick to the aluminum foil, and the color of wire insulation and sheath went from "white" to "light-almond", really the only way i can describe the color change. the internal paper didnt seem to be affected at all. i tried to slice off some of the wire insulation with a knife (butter knife w/ some not very sharp serrations), but it wasnt soft enough for the knife to grab into.
we would expect any properly installed wire that has good working ocpd to never allow enough amps to get the wire to 300F, and a odd fault that allowed persistent high enough amps to get the wire to 300F i do not think the wire would fail. i suspect if we went days in the oven we would see good discoloration but i dont think that would cause a failure, and arc'ing across the conductors due to compromise in insulation is a low probability, but only formal testing can confirm that.
someone must have it, can share some of its verbiage?? we're not here to profit from it, using it for educational purposes, etc. but i dont think that is the UL # on the SIMpull wire i have. let me check
so, did the insulated wire open air tests. last one right at the top of the 60C column. as before, the probe just sat there until equilibrium was there for about ~10min or so.
note: in this pic the wire is about 1.25" above the table.
ambient air 60F
13.46A 70.7F (21.5C)
26.0A 84.7F (29.3C)
48.15A 137.3F (58.2C), basically feels warm to the touch.
that stated, ambient was different, but the relationship looks like 10F, so i might hypothesize normalization back to 70F ambient as:
13.46A 80.7F (27.05C)
26.0A 94.7F (34.44C)
48.15A 147.3F (64C), basically feels warm to the touch. 3.2x (2.57x more than 125% of rated ocpd) more than NEC's prescribed max amps with temp hitting ~60C. there is no way this temp has potential to start any fires, unless you bring me an example or scenario that you think might.
The test was worth it, but it will take a lot longer for the wire to degrade. One major event indicating breakdown is "plasticizer migration" (worth researching).
There are a few free UL reports that did testing on NM wire as part of over driven staples, I will find them and post them.
<snip>
and just wanted to point out, temp alone doesnt mean too much. its energy that matters. a thin wire that is hot may not have enough energy to get a big piece of wood into that combustion zone, while a big wire that is giving up lots of heat energy at a lower temp than that thin wire could be bad for that piece of wood.
Found the one from UL, starting at page 41 where a controlled degradation test is done by subjecting the wire to high temperatures:
https://www.nfpa.org/Assets/files/AboutTheCodes/70/Investigation_Damage_Degradation_NMCables.pdf