mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
ok, but in the study of forceful destruction i can see why letting it cook for days or weeks is a good educational exercise, but how does this play into the ampacity #'s as we know them today (nec2012)?
It might, it might not in the sense that if the wire does reach an actual temp of 90*C, what happens to it? I did find this, which is food for thought from the AS/NZ code:
The normal operating temperature of thermoplastic cables, including flexible cords installed as installation wiring, are based on a conductor temperature of 75°C. This is due to the risk of thermal deformation of insulation if the cables are clipped, fixed or otherwise installed in a manner which exposes the cable to
severe mechanical pressure at higher temperatures. V-90 and V-90HT insulated cables may be operated up to the maximum permissible temperatures 90°C and 105°C provided that the cable is installed in a manner that is not subject to, or is protected against, severe mechanical pressure at temperatures higher than 75°C. Such applications also allow for cables to be used in—
(a) locations where the ambient temperature exceeds the normal 30°C, e.g. equipment wiring in
luminaires and heating appliances, or in roof spaces affected by high summer temperatures; and
(b) locations affected by bulk thermal insulation that restricts the dissipation of heat from the cable.
It is possible (just a wild guess) that at higher temperatures stapling may play a role with our NM cable being kept out of the 90*C column despite having 90*C insulation. The last parts (a) & (b) might also give hint why 90*C is used in NM despite the CCC restricted to 60*C.
i mean, i can watch romex turn to dust just by leaving it exposed to sunlight during the summer, the UV will destroy it in no time, but this is not very beneficial in developing ampacity #'s. the NEC is about rules and #'s that make sense for proper installation and use with some safety tolerance for faults. i suspect once a wire gets itself into that zone outside of proper installation and use, perhaps by a fault for whatever reason, the ampacity table likely no longer has relevance because the fault, it it were to do damage or create a fire, would do that regardless of ampacity #'s.
i kinda went on tanget with this free air and baking test. those are odd conditions that are likely to not be prevented by way of ampacity #. my sandwich test is to see if a "nec worse case scenario"can produce any crazy temps of the wire, and from there we can evaluate if those temps will be harmful to the surroundings.
I dont think it was wasted effort imo, its always a good idea to know what temperature wire can handle before deteriorating. If anything you are verifying the 90*C claim. Once known you test specimens can survive 90*C, another variable if error is eliminated from the testing.
somewhere out there was a post about a store ceiling catching fire, it was stated that the 240v "romex" line had migrated into the insulation bay in the ceiling and basically covered itself with the blown-in insulation, and thats where the visual damage was, and some had concluded that due to the coverage of the insulation the temps rose too high causing the fire. but oddly, no forensics to see if the wire itself may have been faulty at that location, i could not see why the temps on the wire, even under the loose insulation, would climb so high that it would cause fire. ocpd was not faulty. and sure, the temps may have gone up to start the fire, but perhaps not because it was under loose insulation.
Sounds like this:
http://www.resolvematters.ca/09/images/file/Cable_Ampacity.pdf
Now you are thinking Several electricians who viewed this article in another forum said the same thing: Its possible that the wire overheated from damage rather then insulation suffocation.
so, it is quite impossible to account for all the odd situations that may cause an issue, its just not possible, but what we can do (nec) is write rules and #'s that make sense given proper installation and use. 20A ocpd on #14 romex (either change ampacity #'s or allow the 75C column), seems ok to me (maybe apply voltage drop rule to limit run size, whatever), but we'll see what the sandwich test show for temps, i am not expecting a "oh geez" moment.
Personally, the NEC should develop various ampacity tables based on how the wire is installed. Nearly all electrical codes outside of North America let you do this, and it does pay off for them without incident. I believe the NEC should restrict #14 to 15 amps only where in dense thermal insulation or foam insulation. Where in open air or in a wall without insulation there is absolutely zero risk over the course of 60 years placing #14 on a 20amp OCPD. PVC cables smaller then 2.08mm2 #14 (like 1.5mm2 T&E) are run at 16 and 20amps for decades under such conditions without a single sign of overheating.