The OCV may be to low, but it might work out just fine. The rest sounds ok, especially the thermopaste.
well, ocv doesnt really matter, its a short circuit, we only care about amps. i ran into a slight snafu, with the variac at lowest setting just turning the power on gets me 8.1amps, very little control from the dial, etc. i might put another step down between the variac and mot. not a big issue.
so, i just ran a few tests for open air:
9" length of bare #14 copper (from the Romex i will test with), 0.064"dia
ambient air 70F (big room, no air movement)
i did two tests and let it soak into equilibrium, i'll list the amps here, you guys can guess the temps, since there were some bets going. my CM660 has a TC feature (calibrated with 32F ice water), so i used that to take temp readings by letting the tip of the probe rest on the copper with just a tad of weight to hold them together.
equilib point #1 13.90A temp ?
equilib point #2 26.85A temp ?
post your temp guesses, i be back in just a few.