NM restricted to 60C column under these conditions
- installed in exterior walls
- installed in any space where NM and thermal insulation co-exist
- installed in ceilings or attic spaces where NM is covered/surrounded/touching by insulation for more than 12"
- installed in walls, ceilings, attics such that the NM is enclosed on both sides to form a "closed bay" AND the framing members that form that bay are less than 1.5" in minor dimension
- passes through any wood member where the path of NM is in wood for more than 3"
reasons why?
1) most exterior walls are insulated, if not now then likely later will be
2) takes care of those interior walls that call for insulation for sound or other reasons, or might get insulation later (this one has potential issue because a contractor called in to add insulation will likely not know about the NEC rules, etc)
3) the 12" rule, allow the NM to pass across/through insulation section in order to reach destination. this has to be a cumulative rule so that installers cant bob the NM up/down through insulation, like under for 10", then out into air for 1", back under for 10", etc etc.
4) this cavity rule so that NM cant be enclosed in very small space that has no insulation, providing enough air in the bay to keep temps down. maybe turn this into a fill % # which would also handle the case of more than one NM in same bay/cavity.
5) for things like top plates were it might be more than two 2x4's, sistered members to form a post, 4x4, etc
i guess if we didnt have CT in the breaker panel we could have access to the power with lower temps on the wires. hmmmmm, who has done this before?