Which doc though?
UL 489 specifies the trips.
Eaton TB01200003E.pdf has their trip curve. max-min for x1.25 is within UL 489 testing for UL 489 ambient of 40C. sadly, its done under one temp only, there really needs to be a UL test that has several ambients, perhaps three below and three above 40C, like 10/20/30/40/50/60/75
UL 489 Parameter
Calibration
100% of rating – hold
135% of rating - trip in one hour (<50A)
200% of rating - trip in 2 min. max. (<30A)
so, lets say 20A on ~#14. in US thats 2400VA, in UK its 4800VA !!As an example, BS7671 which applies to the United Kingdom: 2.5mm2 (slightly larger then 2.08mm2 14 gauge) Twin and Earth (Euro equivalent to romex) is rated 27 amps when stapled to a wood stud having no insulation, 20amps when one side of the cable is resting against insulation and 13.5 amps with the cable completely covered in insulation. The conductor operating temp is assumed to be 70*C. If we were to compare these values to 14 gauge wire, we would roughly get 25 amps, 18.5 amps and 10.5 amps. Thus, the European codes require NM wire to be kept at current ratings lower then our NM wire when completely covered in insinuation and higher rating when not.
so they can deliver 2x the power as we can using "same" wire.
i was saying at 2400VA in UK (which is what we can deliver in US) the amps in UK would be half and thus 1/4 the heat.
does UK have a 4kVA hairdryer? that might melt hair??