I'm not getting the relationship now Mr MBrooke
and i was soOOoo blissful before this thread too....
~RJ~
It goes like this. When a fault at the furthest point relies on thermal trip, there is a delay in heating the bimetal before unlatching takes place which in turn also heats the conductor. If the fault sputters or "arcs" it limits the current acutall increasing the time for the bi-metal to open. So it is necessary to factor in a certain margin of short circuit heating into the wire. However, that value can be substantially reduced on magnetic trip because it is near instantaneous and in turn the wire carries less fault current.