Much smaller I can almost fit my whole hand in a 2 gang mudring
I'm pretty sure that most of us can that's not really the point now is it?
people tend to forget that UL listing requirements and NEC requirements are not the same thing. You have to abide by both. Just like you have to abide by the terms of the contract. if the customer wants his conduit painted pink and it is in the contract it is required even though neither UL nor the NEC requires it.So, if I use UL listed boxes and covers, UL listed wire nuts, and UL listed electrical tape, it's just fine to bury all the boxes I want behind drywall?
I was trying to make the converse point. UL may have approved the receptacles, but if you can't get to the splices or whatever else you need to do, like a ground connection to the box, you won't pass NEC muster. So the contract may require them, but if you can't produce a code-compliant installation you can't use them. Final decision is up to the AHJ. If you can convince him or her, go for it.people tend to forget that UL listing requirements and NEC requirements are not the same thing. You have to abide by both. Just like you have to abide by the terms of the contract. if the customer wants his conduit painted pink and it is in the contract it is required even though neither UL nor the NEC requires it.
that is pretty much what I said.I was trying to make the converse point. UL may have approved the receptacles, but if you can't get to the splices or whatever else you need to do, like a ground connection to the box, you won't pass NEC muster. So the contract may require them, but if you can't produce a code-compliant installation you can't use them. Final decision is up to the AHJ. If you can convince him or her, go for it.
OK, I guess I'm just a little thick today.that is pretty much what I said.
You don't necessarily need to get your hand in the hole as long as the wiring (splices) can protrude thru the opening
Did the inspector raise any of the issues discussed here or something else entirely?Just literally had an inspection 10 minutes ago. Inspector failed it
Sent from my SM-G986U using Tapatalk
But what if customer wants it painted pink but UL or NEC prohibits it? (not saying it does but what if it did)people tend to forget that UL listing requirements and NEC requirements are not the same thing. You have to abide by both. Just like you have to abide by the terms of the contract. if the customer wants his conduit painted pink and it is in the contract it is required even though neither UL nor the NEC requires it.
Then somebody else, not the sparky, gets to take credit for the violation. If I were the sparky, I'd provide a letter, politely declining to comply with the customer's request and including the relevant code citations. If s/he wants to hand that chore off to the painter on the project, that's on them.But what if customer wants it painted pink but UL or NEC prohibits it? (not saying it does but what if it did)
Two pigtails?I don't know how you would get at the splices when you have more than one device in a box
Agreed.IMHO it is compliant to not have access to the cover mounting holes.
What is required is access to the splices. If the rough were done with proper consideration for providing access to the splices, then it would be completely fine. As the OP describes it, the rough was done and _then_ the customer asked for these devices, making it difficult/impossible to do properly.
As I see it, access to the cover mounting holes would be an alternative means of gaining access to the splices. So if the rough is not properly done to permit you to pull the splices out through the holes (as described in the device instructions) _and_ you don't have access to the cover mounting holes as a way to work around that issue, then you have a non-compliant installation.
-Jon
Here it is still my permit and possibly my contactor license that are impacted by violations if I refuse to make corrections and/or not pay the reinspection fees that will be charged, so I am at very least explaining this to customer beforehand, if that don't work I can get inspector involved early on and hopefully can get a resolution of what will or will not pass. Inspector can inform them he has authority to order POCO to disconnect service if the installation does not comply with NEC. This will at least get customer off my back since they now realize there is someone else holding up what they want done and not just me.Then somebody else, not the sparky, gets to take credit for the violation. If I were the sparky, I'd provide a letter, politely declining to comply with the customer's request and including the relevant code citations. If s/he wants to hand that chore off to the painter on the project, that's on them.