That wasn't the question though. See posts 137 and 131.No matter the measurement device, generation is not dissipation.
Mark
That wasn't the question though. See posts 137 and 131.No matter the measurement device, generation is not dissipation.
Mark
Ok thanks.
- Did they recheck the current on the neutral now that transformer has been replaced? - YES
- Does the utility use TWACS metering? - NO
- Do the lights still flicker after transformer has been replaced? - YES
- Do the lights still flicker with incandescent bulbs? - DID NOT TEST THIS THOUGHT.
120/240V residential.Is this a 120/208V system where the L1-N and L2-N voltages are 120° apart?
is the 10A from the same load?Test...
All L2 circuits Off
L1 = 10A
L2 = 0
N = 10A
All L1 circuits Off
L1 = 0A
L2 = 10A
N = 10A
One 20A branch circuit on L2 On
L1 = 10A
L2 = .5
N = 10.5A <----- Shouldn't this be 9.5A?
Current Reading at time of typing:
L1 = 1.1A
L2 = 5.6A
N = 5.5A <---- ??
Will do...If you can, I suggest putting a clamp meter on the L1 and L2 conductors together, in addition to your L1, L2, and N measurements. The line side of the L1 and L2 conductors should be on the same side of the clamp opening.
If possible, you could also put the clamp around all three conductors L1, L2, and N, and then see what you get.
Preferably, you would make some measurements with significant currents (say around 10A) on both L1 and L2, but the currents wouldn't need to match.
Yes. We swapped the coffee pot from one circuit receptacle to another circuit receptacle.is the 10A from the same load?