bobby ocampo
Senior Member
What is the importance of connecting the neutral to the earth or ground?
bobby ocampo said:What is the importance of connecting the neutral to the earth or ground?
Isn't it that if neutral is not connected to ground it is considered ungrounded system? If connection to neutral is of LESS IMPORTANCE then why do we have a SOLIDLY GROUNDED SYSTEM?iwire said:IMO in regards to premises wiring systems operating under 600 volts the connection of neutral to dirt is of much less importance then the connection of neutral to the equipment grounding conductor.
And of course I should make clear my post are only aimed at solidly grounded systems.
bobby ocampo said:And if neutral is not connected to ground then we should use a two pole circuit breaker because neutral will be ungrounded current carrying conductor?
bobby ocampo said:Isn't it that if neutral is not connected to ground it is considered ungrounded system? If connection to neutral is of LESS IMPORTANCE then why do we have a SOLIDLY GROUNDED SYSTEM?
bobby ocampo said:why do we have a SOLIDLY GROUNDED SYSTEM?
iwire said:You have been working on substations which I imagine use a multi-ground neutral which is different from premises wiring which use separate grounding and grounded conductors.
don_resqcapt19 said:Solidly grounded just means that one of the circuit conductors is connected to earth without any intentional resistance or impedance.
Additionally, a floating supply system (i.e., ungrounded) will typically show the same voltages to earth as a grounded system with a high-impedance voltmeter due to capacitive coupling with the earth and nearby grounded surfaces.bobby ocampo said:What is the importance of connecting the neutral to the earth or ground?
peter d said:Which connection is more important in your mind? A connection to earth of an unknown impedance? Or a connection back to the source via a metal conductor (bonding jumper)? Which will facilitate the quick operation of an OCPD?
roger said:Per the 2008 NEC we have to use a multi-pole breaker or handle ties with all circuits that have a neutral whether it is connected to earth or not.
In earlier code cycles this was not always the case.
Roger
bobby ocampo said:Can you site specific provision of the 2008 NEC where it is now require to use two-pole circuit breaker for line to neutral load if the neutral is grounded?
iwire said:Ahhh, now I think I see the issue.
We are not using the term 'solidly grounded' in the same way and I don;t know which one of us is using that term correctly.
To me the solidly grounded means a solid connection between a line conductor and the equipment grounding conductor. The term solidly grounded does not refer directly to the connection to the earth.
You have been working on substations which I imagine use a multi-ground neutral which is different from premises wiring which use separate grounding and grounded conductors.
bobby ocampo said:What is the importance of connecting the neutral to the earth or ground?
don_resqcapt19 said:Solidly grounded just means that one of the circuit conductors is connected to earth without any intentional resistance or impedance. As far as calling the system a "grounded system" the connection to earth is very important.
don_resqcapt19 said:As far as the importance of the connection to earth for system operation and safety on under 600 volt systems, it is not as important as the system bonding connections.
LarryFine said:I typed up a little ditty a while back that may help explain grounded neutrals a bit:
http://forums.mikeholt.com/showpost.php?p=708650&postcount=4
roger said:Yes I can, but first, can you tell me where in the NEC a neutral conductor is required to be, or allowed not to be, bonded to the GEC?
Roger