If the terminal bar is the MBJ, exactly how is it between the grounded conductors and the EGC/enclosure?
How is it NOT? :lol::huh:hmy::roll::?
(Also you keep adding that 's' that isn't in the code. It's the grounded service conductor only.)
BTW, I forgot to make the following comment earlier.
So do we get to selectively determine Code compliance based on whether an issue makes no difference to safety or functionality?
Simplest answer: yes. The code gives such authority to an AHJ in 90.4, at least with respect to safety (not so much functionality). Moreover, the code has a purpose which is described in 90.1. When interpreting code requirements it is correct and reasonable, in my opinion, to consider the purpose of the code in the course of interpretation. This of course does not give either AHJs or (especially) contractors license to willfully ignore whatever code section one wants. But neither does the code call for itself to be enforced to the nitpicky letter without regard to its purpose.