Well, ID say this: those circuit breakers that passed power but no GFI protection it was because a lost hot or neutral did it? And those GFCIs that had power they could not test or reset, correct?
FPE breakers have been known to jam shut and stay closed- whether this is due to it being reset after a trip, or jamming anyway after being first turned on and not responding to a trip in the first place, IDK. Very hairy on old split bus or main lug only panels w/ no main (the fpe main had its problems too, but at least there would have been the one extra layer of protection, albeit at a higher trip rating).
I believe that the GFCI lockout is a newer conception-many older gfcis with failed electronics continued to provide power when the test button was pressed.
I have to agree that newer receptacle style GFCI's are better at locking themselves out from some failures, and have had listing requirements for some of those changes.
I don't think they have done much to circuit breaker type GFCI's though when it comes to locking them out when there is no protection or compromised protection.
If this were a true life safety device they would have more failsafe features and would cost a lot more then they do.
There are not a lot of FPE breakers around here, but I have never run into one that fails to open when switched. If would I run into one that failed to trip when required there was probably a fire. Long time ago we did have a house fire nearby that had a FPE panel, house was a total loss. Fire started at an appliance, but do not know if FPE breaker was a contributing factor or not, just was reported there was a failure in that appliance.