I was talking no threads like how we use thread less connectors, or EMT connectors with just a set screw.
H'mm then your not filmilure with bonding lock nuts? grounding bushings? they were created for this purpose?
There have been many things brought out into the market place over the years that didn't have a real requirement or purpose that was needed for additional safety, a few of these found their way into code requirements not because of it provided a bigger margin of safety but because no one did any research to see if it added any safety to the existing design of the installation, while this connector could find good use in maybe an installation in an optional robust bonding scheme for lightning protection, and I can see where bonding at the cabinet can prevent arcs of high energy high frequency lightning strikes will give a little more contact to dissipate this current, and maybe prevent damage to the area where a GEC passes through the cabinet but for but for the most part they will not create any extra help for normal current paths or faults, the requirements in the NEC (70) does nothing to very little in lightning protection, as I have posted many times before, and test at camp blanding serve to back up this point of view, I think it was Brian who posted the original camp blanding report on this back in 2006.
Bonding locknuts (the ones with a single setscrew) were developed for environments with high vibration to prevent the locknut from loosening. Some have pushed them as supposedly having greater current carrying capability. I don't agree. They just make the connection to the cabinet more reliable by preventing the locknut from loosening. I don't know of any AHJ that doesn't 'trust' a properly installed locknut to do its job. However, I am sure there are some out there.
As for bonding bushings, Bounding Bushings were developed back in the late 60's by O-Z/Gedney and other mfr's. In fact, O-Z/Gedney had one of the first iterations of the traditional bonding bushing we see today. Their patent #3,706,959 describes the 'need' below:
Grounding lugs for conduit fittings such as disclosed in the prior Browne U.S. Pat. No. 3,365,693, issued Jan. 23, 1968, are provided primarily for facilitating the grounding of conduit through a conduit bushing threaded onto the end of conduit, as at a service box, where the conduit passes through a wall of the box. Lugs of this type are generally adapted to be secured by a single screw to the periphery of the conduit bushing, and are adapted to receive a ground wire, preferably without requiring the wire to be cut. A clamping screw is provided for securing the wire within the lug. Heavy ground current can flow through the lug under abnormal conditions, as because of phase to ground faults and the like, and thus it is important that the lug provide a low resistance connection from the conduit and service box to a substantially heavy ground wire.
One of the problems encountered with connectors of this type is that the lug may be loosened in insertion and tightening of the ground wire due to rotation of the lug in relation to the bushing. Such turning can also be caused in certain types of bushings having a ground screw at one side of the lug when such ground screw is tightened against a wall of a housing. The tightening of such screw has a tendency to rotate the lug and thus loosen the screw fastening the lug to the periphery of a bushing, resulting in a poor connection between the lug and the bushing.
It has also been found that a loose connection can develop within the lug due to initial cold flow of the wire conductor material caused by plastic yielding of the metal under pressure applied by the clamping screw used to secure the wire within the lug. This problem is accentuated by thermal expansion of the conductor in an unyielding lug body, upon passage of high short-circuit current; the deformation of the conductor then results in a poor connection upon cooling of the two.
An object of the present invention is to provide an improved ground device for a conduit which substantially obviates the disadvantages of the described prior arrangements.
Another object of the present invention is to provide an improved ground device for conduit wherein a grounding lug is positively prevented from rotating relative to its associated bushing.
Another object of the present invention is to provide a grounding device for conduit having spring loaded contacting portions for ensuring maintenance of low resistance connections.
In some switchgear applications, these grounding bushings are specified in the installation because they allow an even greater ground fault current to be passed through from the conduit to the OCPD. A standard conduit and locknut setup only has a certain amount of current carrying capability, which is sometimes limited by workmanship issues such as insufficient torque, poor cleaning of enclosure KO paint, or crooked conduit entry - which does not allow the locknut to sit flat. The bonding bushing takes a lot of the uncertainty and variability away.
Current carrying capability is determined by the total cross-sectional area, impedance of the material, contact area/pressure, and max temperature allowable with a specified current flowing through. By adding these grounding bushings, along with the specified bonding conductor, the effective current carrying capability has been increased, and has not been limited by the enclosure, nor the connection between that and the conduit locknut.
I know in our own internal ground fault current tests, especially with our new MC fitting, we have seen the box fail before the largest size conductor or the fitting. This was due to a large amount of amperage (5500A+ for 9s) and a relatively thin box wall (.062").
In the end, there are so many AHJ's out there that have their own interpretation of what should really be a 'unified' standard. They want what they want, sometimes without support of the NEC. Just look at Chicago and their absolute 'distrust' for any NM, AC/MC, or FMC. It is either an EMT or RMC install - period. It does not matter to them if the rest of the country is wired up in cable.