Under the 2017, individual 15A circuits for a dedicated appliance can be installed in areas covered by the SABC rules. Does not have to be just refrigeration equipment anymore.
210.52( B)(1)
Old exception:
Exception No. 2: The receptacle outlet for refrigeration equipment shall be permitted to be supplied from an indi- vidual branch circuit rated 15 amperes or greater.
New exception:
Exception No. 2: In addition to the required receptacles specified by 210.52, a receptacle outlet to serve a specific appliance shall be permitted to be supplied from an individual branch circuit rated 15 amperes or greater.
I find this and interesting and what I consider perhaps slacking requirement in the code. It used to be that basically all receptacles in the kitchen and other 210.52 mentioned areas had to be fed from the two small appliance Branch circuits, exceptions withstanding.
Now according to the 2017 as I am reading it for the first time, you may have individual branch circuit feeding a single receptacle in the kitchen in addition to the required small appliance Branch circuits.
I have absolutely no idea aside from something like a built-in microwave which already requires its own circuit, or the refrigerator cut out, which will be obvious, how one would determine Appliance needs on a countertop to install these 15 amp or greater branch circuits.
I do not see a problem with adding more branch circuits to a kitchen, regardless of amperage, however I think the code would have been better served just to simply mandate three or more 20 amp SABCs to serve receptacles covered by 210.52.
if I am building a higher-end kitchen, why would I even mess with 15 amp dedicated receptacles to equipment that does not exist? Even if the homeowner told me "hey I'm going to put a Fry Daddy here or a Keurig coffee pot there", it cost next to nothing more to go ahead and make those 20 amp circuits and be done with it.
As for countertop microwave versus built-in, one is more or less permanently mounted, one is not. to put it another way, if there is no built-in microwave, you do not have to wire for it. Honestly, it is not an NEC issue what the homeowner plugs into the code required small appliance branch circuits, that is a design issue, and the NEC is not a design manual.
Now, let's open up the debate on whether the 2017 NEC exception for single receptacle outlet means simplex receptacle.:lol: