Kwired, you raise a good point, but, in my humble opinion, you buried the lead. I believe you are considering Fluorescent Strip Lighting (or equiv.) wired end to end.
The Lighting Outlet has Branch Circuit conductors ending in it. The wirenut splice between the Branch Circuit conductor and the Luminaire conductor houses the Outlet. It could be up in the box, or down in the canopy or other cavity of the Luminaire body.
Here you are describing a SINGLE luminaire.A luminaire with the supply wiring method directly entering the luminaire - that point is within the luminaire, but exactly where within the luminaire may also be a little debatable. Is it the point of entry of supply conductors?
The Lighting Outlet has Branch Circuit conductors ending in it. The wirenut splice between the Branch Circuit conductor and the Luminaire conductor houses the Outlet. It could be up in the box, or down in the canopy or other cavity of the Luminaire body.
Yes.Is it at the point where supply conductors connect to conductors that came with the luminaire?
This is clouded by the "run of linear luminaires" being rated as RACEWAY and therefore housing Branch Circuit conductors. The splice between the Branch Circuit conductors and the Luminaire conductors is the Outlet, so there are multiple outlets.If you have a continuous end to end run of linear fixtures don't you have supply conductors and an outlet within in each luminaire?