M. D.
mpd said:even if you bond the sprinkler piping, do the sprinkler fittings effectively bond the sections of pipe?
What would be likely to energize it??? even if it is isolated
M. D. said:What would be likely to energize it??? even if it is isolated
LarryFine said:I've always wondered how one instructs a non-isolated bonded sprinkler piping system to not behave as a grounding electrode?
DanZ said:http://www.mikeholt.com/newsletters.php?action=display&letterID=191http://www.mikeholt.com/newsletters.php?action=display&letterID=191
http://www.mikeholt.com/newsletters.php?action=display&letterID=26
http://www.mikeholt.com/mojonewsarchive/All-HTML/HTML/Grounding-vs-Bonding-Online-Training-5~20050715.php
http://www.mikeholt.com/mojonewsarchive/GB-HTML/HTML/Grounding-versus-Bonding-Part-2-of-12~20041014.php
Does any of this help?
RyanJackson said:Alright. I just got off the phone with the UL rep from panel 5, and we talked about my proposal. The proposal was rejected, but thats OK, because I knew it would...I was just hoping for a panel statement to answer the issue.
Anyway, according to panel 5, if the sprinkler piping is a metal system it is a 250.104(A) (water) installation. If it is broken up with nonconductive couplings, it is a 250.104(B) (other) installation.
Ryan Jackson
Salt Lake City
Inspector, Instructor,
Code Consultant
5-240 Log #1448 NEC-P05
Final Action: Reject
(250.104(B))
____________________________________________________________
Submitter:
Ryan Jackson, West Valley City, UT
Recommendation:
Revise as follows:
(B) Other Metal Piping. Where installed in or attached to a building or
structure, metal piping system(s), including gas piping and fire sprinkler piping
, that is likely to become energized shall be bonded to the service equipment
enclosure, the grounded conductor at the service, the grounding electrode
conductor where of sufficient size, or to the one or more grounding electrodes
uses. The bonding jumper(s) shall be sized in accordance with 250.122 using
the rating of the circuit that is likely to energize the piping system(s). The
equipment grounding conductor for the circuit that is likely to energize the
piping shall be permitted to serve as the bonding means. The points of
attachment of the bonding jumper(s) shall be accessible.
FPN: Bonding all piping and metal air ducts within the premises will provide
additional safety
Substantiation:
There is a long-standing debate as to whether fire sprinkler
piping is a 250.104(A) or 250.104(B) type of piping. I have spoken with
several code experts on this issue, including multiple members of Panel 5, and
have received different answers on this issue. Accepting this proposal would
end this debate, and would be a step forward in the uniform interpretation of
this rule, which is something that we should all be striving for.
Panel Meeting Action: Reject
Panel Statement:
A metallic fire sprinkler piping system is metal water piping
system that is covered by Section 250.104(A). Section 250.104(A) does not
differentiate or exclude between the various types of metal water piping
systems that might be present in a building or structure. Section 250.104(B)
covers metal piping systems other than those metal water piping systems
covered by 250.104(A).
Number Eligible to Vote: 15
Ballot Results:
Affirmative: 15
LarryFine said:So we don't need a bonding jumper based on the service size, like the water piping does, but only sized for the circuit likely to energize the piping, if there even is one.
LarryFine said:So, what circuit is likely to energize a sprinkler system? Who determines whether there is such a circuit in any given installation, say with no fire pump or alarm circuit?
There very well may be no such circuit, meaning that bonding sprinkler piping is clearly not a universal requirement.
dnem said:... But that throws me right into an electrode vs general bonding conversation with a fire marshall. . I honestly doubt he understands the difference and I don't know if he's open to learn anything from an electrical inspector.
dnem said:If it has nonconductive couplings, then you go to 250.104(B) and the "likely to energize" wording.
dnem said:There's no clear way to determine if such a circuit is present and which circuit is the "likely" one. . We always handle 250.104(B) the same way. . Ignore your service disconnect size, pick the largest OCPD in the building [feeder or branch circuit] and size according to that.
Other metal piping systems such as gas or air that are likely to become energized must be bonded to an effective ground-fault current path. The equipment grounding (bonding) conductor for the circuit that may energize the piping can serve as the bonding means. (See NFPA 54, National Fuel Gas Code) Because the equipment grounding (bonding) conductor for the circuit that may energize the piping can serve as the bonding means, no action is required by the electrical installer.
It should say "... no additional action is required ..." :smile:M. D. said:Because the equipment grounding (bonding) conductor for the circuit that may energize the piping can serve as the bonding means, no action is required by the electrical installer.
In mine, too.If you can't determine what that circuit is ,.. then it is not likely to be energized ,..IMO
M. D. said:That is very conservative to say the least,.. do air lines ,.gas pipes , air ducts ,.. waste pipes ,..get treated the same??
M. D. said:So your office does not agree with this depiction
Why? What is likely to energize the water heater or hot-water piping?dnem said:The hot water tank in that picture does not appear to have a blower motor so 250.104(B) would require an additional bond for the hot water pipes.
LarryFine said:Why? What is likely to energize the water heater or hot-water piping?
dnem said:The hot water tank in that picture does not appear to have a blower motor so 250.104(B) would require an additional bond for the hot water pipes. . Since the cold is already bonded to the service [assumed], a hot to cold jumper is all that is needed. . We would tell the contractor to size it according to 250.122 and according to their largest amp breaker, service main excluded.
If the hot water tank did have a motor of some type, then the equipment ground of the motor provides the bond and has already been sized for the motor circuit that it feeds. . So it with usually be allowed to be smaller than a motorless pipe system bonding jumper.
In the real world, the largest breaker in most panels [excluding the main(s)] is usually 300a or less. . 250.122 for 300a is only #4 which is common everyday stuff and also fits in your standard size pipe bonding clamp.