Mike,
Before I comment on anything you posted, I want to make sure that were in agreement on what all of the "pieces parts" of grounding are. . Because if you intermix the categories, all you end up with is confusion.
1]
electrode grounding [main coverage in 250part3, 250.50-250.70]
2]
equipment grounding [main coverage in 250parts6+7, 250.110-250.148]
3]
equipotential bonding [main coverage in 547.10,680.26,+682.33]
4] general
bonding [main coverage in 250part5, 250.90-250.106]
and this thread concentrates on subdividing general bonding into 2 subcategories
a] continuous electrically conductive water pipe system [250.104(
A)]
b] not continuous electrically conductive water pipe system and non-water systems [250.104(
B)]
c] isolated structural steel [250.104(C)] is a third subcategory which isn't being discussed at all
For keeping it clear what I'm referring to, I'm going to keep referring back to these categories.
jwelectric said:
Could you please explain to me what bonding one piece of pipe with a 3/0 copper conductor knowing that it has no current carrying ability beyond itself and it possibly being less than one percent of the system would accomplish?
By T250.66, 3/0 for an over 1100kcmil service would be appropriate for a connection to an
electrode [which I listed above as
category #1]. . It would also be appropriate for a general
bonding connection to a continuous electrically conductive water pipe system [which I listed above as
category #4 and subcategory
a, 250.104(
A)].
It would
not be appropriate for a general
bonding connection to a
non-continuous electrically conductive water pipe system or non-water system [which I listed above as
category #4 and subcategory
b, 250.104(
B)].
When you say "one piece of pipe", you're talking
category #4 + subcategory b, 250.104(
B).
By T250.122, for this one piece of pipe you could be bonded with a #4gauge as long as the "likely to energize" circuit is no larger than 300amp. . It's extremely uncommon to distribute runs protected at over 300a that also include a junction box in the run.
So you're bonding with a #
4gauge because of the category and subcategory.
jwelectric said:
Why do you think that the Code Making Panel made the statement they did in the proposal posted above?
I have a ? inch rigid conduit buried 36 inches deep going out to a piece of electrical equipment in the back yard. Do I need to bond this conduit with a #6 as it fits the description found in 250.52(A)(5)(a) and installed as outlined in 250.53(G)?
" going out to a piece of electrical equipment in the back yard"
and obviously containing circuit conductors to that equipment does
not fit the description in 250.52(A)(5)(a). . That ? is a
raceway and can be used as an
equipment ground. . You have to go to Article300 for installation. . 250.52 applies only to
electrode grounds.
Do the electrons flow differently because you label the pipe differently ? . Of course not. . But the NEC says one is an
equipment ground and the other is an
electrode ground and you install them differently and for different purposes.
jwelectric said:
As outlined in 250.118 the conduit itself is an equipment grounding conductor so does that fact make the conduit an electrode?
Never is it
both equipment ground and electrode ground ! . It is always only categorized as one or the other depending on usage and is installed according.
jwelectric said:
If the transformer shorted from primary to secondary or a high voltage line fell across a service drop would the higher voltage cause the NM cable to energize a metal pipe?
"the transformer shorted from primary to secondary or a high voltage line fell across a service drop"
would be handled by an
electrode conductor that is grounded to an electrode.
"cause the NM cable to energize a metal pipe"
I'm assuming this is your backyard ?" pipe, which is an
equipment ground. . The equipment grounding conductor ?" pipe is not there for large overvoltage spikes.
The
electrode ground is installed to handle your high voltage spike and is sized accordingly. . The
equipment ground is installed to handle your NM short or fault and is sized accordingly. .
Don't intermix them.
I'm assuming your next statement is no longer looking at the ?" conduit outside but we're back to the inside pipe, probably sprinkler.
jwelectric said:
My question is why would anyone bond something that isn’t electrically continuous with such a large conductor for in the first place?
"isn’t electrically continuous"
non-continuous electrically conductive water pipe system or non-water systems,
category #4 and subcategory
b, 250.104(
B)
"with such a large conductor"
250.104(
B) sends you to 250.122. . You usually get a
4gauge. . That's not large.
jwelectric said:
Is it the train of though a short time occurrence such as a spike or lightning the bonding would bring everything to the same touch potential? If nothing is connected to something that is metal how is the spike or lightning going to energize it?
If the thought is the touch potential or that everything becomes somehow mysteriously energized wouldn’t we need to ensure that the entire sprinkler system be electrically continuous?
You're mixing 2 things that should not be mixed. . The "spike or lightning" is handled by the
electrode ground [250.50-250.70]. . The non- electrically continuous sprinkler pipe is handled by general
bonding [250.104(B)] and protected from the "circuit likely to energize", not from spikes or lightning. . Don't size the bonding for the non- electrically continuous sprinkler pipe with lightning in mind. . When the code goes to T250.66, it's addressing stuff like lightning. . Size it with "circuit likely to energize" in mind. . You'll be in T250.122.
What makes this tough is that
all of these grounding categories all tie together at the service and are electrically continuous. . There is electrical continuity between electrode grounding, equipment grounding, equipotential bonding, and general bonding.
In real life, the distinction between the categories of grounding doesn't
prevent lightning for ever tracking down any given path and thru the sprinkler pipes. . But that still doesn't allow you to
blur the categories when you are installing the different requirements.
For good or bad, this is how the NEC is set-up. . The fact that all this grounding interconnects doesn't allow you to
blur the categories when you are installing the different requirements.