All I was trying to say in that particular instance was that the presence of water does not automatically indicate gaping holes in the insulation. I have already voiced my own opinions about the water in previous posts. What I know for a fact is that every how-to manual I can find regarding insulation resistance tests say repeatedly that everything must be clean and dry.
My position, were I in iwire's place, would be this (again this is my own opinion and nothing more):
The insulation tested poorly. We can
1) purge with Nitrogen and try the test again. If it passes now, the water was the problem and the problem is solved. I have saved the time and trouble of replacing the cable when it was unnecessary. If it still doesn't pass then we can still replace it and will have only lost the time and money it took to perform the purging. Proceed to step two.
2) Send the wire back to the manufacturer. This will take some amount of time that in any case will be significantly greater than purging the cable with Nitrogen. Time is money, so even if the manufacturer replaces it at no cost I will have lost the time it takes to drive a truck from the plant to me, assuming there is more cable like mine sitting around ready to be sent out. If not, I also have to wait for it to be manufactured.
I don't see what would be lost by trying the Nitrogen purge.
After reading this again, I don't understand. Is the water a problem or not? If purging the water out fixes the problem then the water WAS the problem. If there is a terrible problem with the insulation, it will test bad full of water or not, right? Seems like you're arguing both points here. If the water is the problem then the solution is to find where the water is getting in and stop it. The entry point cannot be poor insulation or blowing out the water wouldn't have fixed the megger reading, right? What you are admitting is that the water in the cable is the reason it megged bad, and you are therefore agreeing with me.

Its nice to have someone on my side here. :wink: